gotcha,, thank you.An MCB operates on over-current, it doesn't care where the current is flowing to, if there's too much current flowing the MCB will operate.
MCB's operate on Live to neutral, live to earth and live to live faults.
Discuss Outdoor and indoor lighting on same circuit in the UK Electrical Forum area at ElectriciansForums.net
gotcha,, thank you.An MCB operates on over-current, it doesn't care where the current is flowing to, if there's too much current flowing the MCB will operate.
MCB's operate on Live to neutral, live to earth and live to live faults.
Even if you did arrange a new circuit for the outside lights, the fault would need finding anyway as things definitely won't be up to the standards required to sign off a new circuit as it stands.The issue with the MCB tripping only seems to happen when I turn on the garden lights, so there is something wrong with that part of the circuit....
[.....] There are maybe 10 garden lights outside.
Thanks for this and all replies. I learn a lot posting here (although I’m starting from a low base!).Even if you did arrange a new circuit for the outside lights, the fault would need finding anyway as things definitely won't be up to the standards required to sign off a new circuit as it stands.
A decent sparks could do some testing to work out where the issue is and I'd imagine have a good idea what is going in within a couple of hours.
One serious point - they aren't RCD protected, and there's a suspected live-earth fault. I'd suggest leaving them off until this is sorted. If they are metal then one or more of them could be in a condition that if they were touched they would cause an electric shock.
It depends on the type of Earth, but as long as >6A fault current can flow from L to E, it can still trip an MCB!But the circuit doe snot have RCB protection...I thought a MCB would not trip from simply a live to earth fault - wouldn't you need an RCB or RCBO? thanks