Hi All,
I have an Halogen Floodlight wired to a 20A JB situated on an external wall with no IP4X protection. I intend on ripping it out and rewiring it and replacing the floodlight with an LED alternative.
However the issue I am having right now is regarding the cable.
I planned on using H07RN-F or H05RN-F cable. This is because both of them are rated for outdoor use, can deal with UV exposure and both can handle the typical temperature range.
However with both of these flex types they only seem to be commonly available in 0.75mm or 1.5mm
1.5mm will not fit through the cable gland into the light fitting. normal VV-F wont fit, so i doubt RN-F will.
0.75mm is only rated at 6A, the light needs to be fed from the Lighting Circuit, which is protected by a 6A MCB (Split load CU so there is RCD protection). As the MCB will never trip exactly at 6A, I believe the 0.75mm cable is not acceptable as there is the potential (though unlikely) that the cable could overheat and burn out before the MCB trips.
So really i need to find some H05/H07RN-F 3G1 cable (3 Core, 1.0mm CSA)
But i cant seem to find it anywhere!
Local wholesalers have claimed they do, ive turned up to buy it and it has been H05/H07 "RR-F" and not "RN-F" one supplier tried to palm me off with VV-F saying it was rated for outdoor use.
Looking at Datasheets from LAPP etc, the RN-F seems to be the only type with a manufactures rating for outdoor use. RR-F does not have a manufactures rating for Outdoor use, but it is still a rubber coated flex cable, Would RR-F be acceptable?
thanks,
Taylor
I have an Halogen Floodlight wired to a 20A JB situated on an external wall with no IP4X protection. I intend on ripping it out and rewiring it and replacing the floodlight with an LED alternative.
However the issue I am having right now is regarding the cable.
I planned on using H07RN-F or H05RN-F cable. This is because both of them are rated for outdoor use, can deal with UV exposure and both can handle the typical temperature range.
However with both of these flex types they only seem to be commonly available in 0.75mm or 1.5mm
1.5mm will not fit through the cable gland into the light fitting. normal VV-F wont fit, so i doubt RN-F will.
0.75mm is only rated at 6A, the light needs to be fed from the Lighting Circuit, which is protected by a 6A MCB (Split load CU so there is RCD protection). As the MCB will never trip exactly at 6A, I believe the 0.75mm cable is not acceptable as there is the potential (though unlikely) that the cable could overheat and burn out before the MCB trips.
So really i need to find some H05/H07RN-F 3G1 cable (3 Core, 1.0mm CSA)
But i cant seem to find it anywhere!
Local wholesalers have claimed they do, ive turned up to buy it and it has been H05/H07 "RR-F" and not "RN-F" one supplier tried to palm me off with VV-F saying it was rated for outdoor use.
Looking at Datasheets from LAPP etc, the RN-F seems to be the only type with a manufactures rating for outdoor use. RR-F does not have a manufactures rating for Outdoor use, but it is still a rubber coated flex cable, Would RR-F be acceptable?
thanks,
Taylor