A collegue at work has asked about having a PIR light added. Not sure if im allowed to do it but said that i would have a look into it. The Consumer unit has no RCD and is the old wylex unit that is found in so many authority houses (meteral i think / skelton type)

my thoughts would be to take power from existing power circuit to FCU, drill through wall and run 1.5mm black flex in 25mm pvc conduit to light.

Will the light require RCD protection?
 
the light won't need RCD protection. the cable would if buried < 50mm deep in a wall. if you can fit your FCU alongside a socket, then drill through the back of the FCU through the wall, then no RCD is required. fit a 3A fuse. the black flex can be clipped or in conduit. if in conduit, you will have problems with cable entry in light fitting unless you fit adaptable boc to conduit, then stuffing gland the flex out to the light. this job would not be classed as notifiable, but you will need to complete a MEWIC. and measure Zs etc. for the circuit you have modified. don't forget that you have to ensure earthing and bonding is in place and adequate.
 
Hi,
I would take the supply from a nearby socket into an RCD fused switch ( make sure fuse is 3amp rated). Then outside to PIR light
If your not qualified to do it, then get a qualified electrician in to carry out the work, just in case you end up hurting yourself.

Not trying to be rude or anything, just helpful advise.

Best regards,
Sav
 

Reply to Outside light in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I'm wondering if it's permitted to replace an outside wall light myself if I use the existing wiring from the old light. In theory I just...
Replies
2
Views
619
What cable would you use to connect this light through a cavity wall to a FCU the other side of the wall? I am thinking, 1.5mm² 3 Core NYY-J...
Replies
6
Views
1K
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
649
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
643
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock