Discuss Oven and cooker circuits in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi i have a double oven which is 5.8kw and induction hob which is 7.4kw there currently isnt a cooker circuit in the house but there is 2 spaces in the CU so am I correct in thinking I can put 2x32A breakers in and run 6mm cable to both .
 
Hi i have a double oven which is 5.8kw and induction hob which is 7.4kw there currently isnt a cooker circuit in the house but there is 2 spaces in the CU so am I correct in thinking I can put 2x32A breakers in and run 6mm cable to both .
Jack a 7.4 KW hob will draw max 32.2 Amps and a 5.8 KW oven will draw Max 25.2 Amps you will need to apply Diversity to those calcs, best advicget an Electrician to design and install circuits to suite the needs.
 
A lot of (sparks) hmm, would struggle with that question, let me remind everyone the new appliances will also come with instructions, now even though as an electrician you should be able to work out the load and cable size, the instructions will also have their own minimum cable size suggested as well lol, that will confuse a lot here, not all of us have enough experience to know what cable is needed automatically or whether one supply is enough for both units.
 
His profile says Quals Part P & 17th so not to be rude to the OP this should be well within what he has been taught. I am hoping that the OP knows the answer but is doubting himself.
That will be all down to Part P then Ant cus the 17th teaches you jack all, except how to pass an exam. Neither qualification will class you as an Electrician. Well maybe it does these days. Part P is a building regulation NOT a qualification.
 
And if the location is the OP''s postcode, then Wales have the stricter Part P rules to contend with too.

I see the OP's been back on and not updated us as yet ............................
 
Caught, not court, didn't you learn owt at school? Court is where he might finish up. **** me the grammar on here doesn't get any better does it, quite apart from the idiot OP's......
upload_2018-5-14_21-8-3.png
we all can't be prefect, can we.
 

Reply to Oven and cooker circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
951
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
198
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
704
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock