hello all, i would be grateful for some advice or pointing in the right direction from someone more knowledgeable and experienced than my not long out of college self.

on a new build, before i had knew what the kitchen appliance specs were, i installed a 10mm cable from board, through cooker switch, to outlet plate and also a single socket off kitchen ring in adjacent cupboard for oven.

the appliances,

siemens 4 ring induction hob - the instructions give the power draw of the rings when on boost, these add up to 7200w. the rating plate on the hob however states I=20a so i'm assuming the hob has an internal limiter. it has an integral 2.5mm flex.

siemens oven -HB13AB550B the instructions say I=16a and this appliance must not be connected with 13a plug, the rating plate on the oven says electrical connection rating 2900w. ( could this be siemens attempt at diversity? ). it has an integral 1.5mm flex.

i want to put both flexes into the outlet plate and protect with an 40amp breaker ( possibly a 32a but they're are moving in just before christmas dinner so maybe not) but the 1.5mm oven flex is making me nervous. i know the flexes are ok for overload protection but i'm not sure how to prove they would be ok under other fault conditions ie short circuit and earth fault.

any thoughts or advice would be appreciated
 
Put both the appliances on a dual Cooker Connection Unit supplied by the 45A cooker switch, and go away sleeping comfortably of a night. You can use either a 40A or 32A breaker, you didn't even need to install a 10mm cable to the cooker switch either, a 32A breaker will comfortably look after any cooking load up to 15KW on a 6mm cable....

Shame you didn't read the multitude of Threads here on exactly the same subject, might even have saved yourself a few bob on materials into the bargain....
 
engineer54, thank you for your response. i have used dual connection units before but only when i could fit a cable to the appliances myself. these appliances have integral flexes that i cannot change. 2.5mm and 1.5mm. if i connected both flexes to the outlet plate and protected by a 40amp breaker, would this be ok? how could i prove that the 1.5mm flex in particular would be ok under fault conditions when protected by such such a large mcb?
 
or fit 2 single sockets on a dual back box. plug each appliance in.
 
adiabatic equation tells me that the minimum size would be 0.55 sq.mm. using a fault current of 200A disconnecting in 0.1 sec.
 
Hmm LOL, if he went to college.

PROUD TO BE A MENTOR IN THE TRAINEE SECTION.

there are some mentors a trainee can do without. you know what happens when you ridicule someone for asking a question? they stop asking questions.

not me though. i'm too old to give a ****.
 
Last edited:

Reply to Oven and hob again in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
712
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
819
Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K
I have a double oven connection unit. Fed with 4mm cable,40 amp MCB. Hob connected to it with 4mm cable. Bought new oven,stated 16 amp but with...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock