Discuss oven and hub switch optional? in the UK Electrical Forum area at ElectriciansForums.net

R

ronoc

Hello there.
I recently had a new kitchen installed. There is a large switch that lights up when switched on above the oven and hob. I thought this switch had to be on for the oven or hob to work. However the oven and hob work if this switch is off or on, it seems to make no difference at all. I asked the installers and they said that due to new regulations the switch has to be now 'optional'.
Can this be true?

Thanks for any help.
Cheers
 
It is an electric oven and hob.
They had to move the switch as I have move the kitchen to another a wall. So it is a whole new install.
 
Errr , possibly 3 x cables at the switch. 1 x feed, 1 x oven, 1 x hob. Possibly wrong connections made within the wall switch.
Check if either appliance actually switches "off" with the wall switch in the OFF and ON positions( ignore neon light if one used)
I got sneaky feeling that only one appliance will be operated by the wall switch. Possibly the oven.
 
Sounds like a BS excuse for a BS job to me. Forgetting the issue of the neon, if a switch doesn't switch then it's not a switch and might just as well be a lump of jam.
 
Then they are bil5hitting you mate, get them back.
And btw the switch should be to the side of the hob, not above it where you need th reach over it to switch off
 
Don't bother getting them to come back.
It sounds like the installer was a cowboy and fed you a line of bull manure.
Get an electrician to come and check it out.
If you can, get one by recommendation. If not get a local niceic or select registered electrician.
 
Don't bother getting them to come back.
It sounds like the installer was a cowboy and fed you a line of bull manure.
Get an electrician to come and check it out.
If you can, get one by recommendation. If not get a local niceic or select registered electrician.

And that would solve the problem?? NICEIC, .... I think NOT!! Most of them will be your Electrical Trainee brigade!!

These day's you can only go by reputation and recommendation from trusted sources!!
 
The OP is in Scotland which would imply that any NICEIC spark is an approved contractor not a DI.
however I do agree that reputation and recommendation is the best way to go.
 

Reply to oven and hub switch optional? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
634
Hi all, I've recently had an oven installed by AO and afterwards I noticed in the installation instructions that the electrical connection needed...
Replies
1
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
824
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock