Good evening

I am fitting in a smeg oven at home and a bit confused with what size off cable it should be installed in and also if it can be safely connected to a fused spur on the kitchen ring or a separate circuit.

The cooker already comes supplied with a flex cable 1.5ml

Looking through the instruction It not very clear what cable size should be used

i have attached pics off the oven instructions. apologise
smeg 1.jpg
smeg 2.jpg
if its a stupid question
 
You say the cooker has a 1.5mm cable fitted. The manual also says to use a 1.5mm cable (under Cable Type).
 
as above separate circuit would be better but it's allowable on a ring as long as other loads are taken into account.
My concern is the gas side, although it's a flueless cooking appliance, with >8kw heat input you would need to check the ventilation and check gas pressures with all appliances running, not as straightforward as the electrical side.
 
and the best tip of the day is.......

install oven in kitchen, as opposed to bedroom.OK that means giving 'er indoors a bit of freedom, but us men do need to eat. :mad::mad::mad:
 
Thanks for the replies. There is no existing cooker circuit in the house yet but the kitchen is get a refurb so should be no problems running a new circuit.

If I was to run a new wire should I increase the size off the cable which was already supplied with the oven ? It has already a 1.5ml flex cable.

At the moment it is wired in to a 13a fuse spur off the kitchen radial protected by a 20amp mcb.
 
i would run a 6.0mm feed off a 32A MCB to allow for ant future upgrades. then connect existing oven to 45A isolator feeding either a CCU or a 13A socket for th time being.
 
Thanks for the replies. There is no existing cooker circuit in the house yet but the kitchen is get a refurb so should be no problems running a new circuit.

If I was to run a new wire should I increase the size off the cable which was already supplied with the oven ? It has already a 1.5ml flex cable.

At the moment it is wired in to a 13a fuse spur off the kitchen radial protected by a 20amp mcb.

There is not need to increase the size of the cable supplied with the oven, you just need to upgrade the fixed wiring the supplied cable is connected to (plugged into).
 

Reply to oven installation tips in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
638
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi all, I've recently had an oven installed by AO and afterwards I noticed in the installation instructions that the electrical connection needed...
Replies
1
Views
1K
I have a double oven connection unit. Fed with 4mm cable,40 amp MCB. Hob connected to it with 4mm cable. Bought new oven,stated 16 amp but with...
Replies
3
Views
2K
The customer has suggested from a previous electrician that the oven requires a new circuit installed . Upon viewing the instructions it is stated...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock