Is it common to see overhead pme systems? I went to a job the other day which had an overhead supply.
The main earthing terminal has the cable coming out of the enclosure and down the wall into the ground.

The external earth loop was 0.26....I phoned the supply authority and apparently they upgraded all the overhead supplies from TT to PME.

anyone else come across this?
 
Quite common nowadays.

They normally PME TT systems at the base of about every 3rd pole and when requested in a domestic situation they can easily supply it.

The supply companies, i believe,have until 2013 to convert most supplies to PME from TT anyway.
 
Does that mean that by 2013, all TT supplies to houses will need to be concentric cable and not separate line and neutral conductors as most presently are ?????

With a TT supply ( separate conductor supply ) , even with PME, isn't there still a risk that should the neutral conductor be broken, you automatically lose your earth ? So PME or not, there's still a risk to the customer.

Can you use an earth electrode to compliment a PME supply ?
 
You are right with the problems of pme it is a cheap fix for the supplyers but if you staked the property and lost the neutral and had a n-e fault ( with most places have) the results would be catosphropic thats why there should be a hold on contactor fitted at the disturbutions side of ervy pme head as like i say the results of a neutral failing is a bad situation to have say a village sub lost a neutral and some one had a neral earth fault the villages load would all try to go through that if they was on the right side of the fault i hope this helps

dazza1212
 
the property i was at had the line and neutral coming in overhead separately, not one cable,
the earth then came out of the earthing terminal and disapeared down the side of the house and into the ground. There are three seperate cables coming out of the enclosue on the wall of the house....
I don't understand how this can be pme?
 
If you have a reading of .26 then i would say that you do have PME.

However, as you probably know, PME is derived out of the side of the head into, normally, an MET.

Can you trace the ME from the CU to see where that goes?
 
I've looked all round the property and have found an old earth rod which has been disconnected.
Other than that i dont know where its going. Where the neutral and earth cables come into the box there looks like some kind of join........theres a transformer at the bottom of the garden which has a cable running down into the ground but i don't know where that goes.
 
Hmmm.

Any chance you can get some pics posted up sometime?

Would be interested to see this arrangement and it also might help us establish whats going on.
 
without sounding rude in any way but did u do a loop with all the bonds disconected,
also where the netral block is at the head is there an earth wire coming out of that to i hope i am not insulting ur inteallagence i only wish to help
 

Reply to Overhead PME in the Australia area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
559
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
664
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
717
I have 6-6-6 triplex overhead that I'm running to a detached garage. At the weatherhead at the garage I'm going to splice 8 guage thhn copper to...
Replies
7
Views
880
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock