Discuss Overhead triplex feeder termination question in the DIY Electrical Advice area at ElectriciansForums.net

ThomasB

DIY
Reaction score
0
I have 6-6-6 triplex overhead that I'm running to a detached garage. At the weatherhead at the garage I'm going to splice 8 guage thhn copper to run down to the sub panel (approx 5' max of 8 guage at both ends of the run). This feeder will be on a 50a breaker.
Does anyone see any issues with this? Everywhere I've looked gives me different answers on the 50a, 8 guage part.
For reference, the 8 and 6 guage are 90°c, and the terminals on the breaker are of course 75°c. 8 guage will be in pvc from the weatherhead to inside the subpanel. Will have a drip loop. Detached garage will have a ground rod. The run already uses 8 guage at the main breaker end which is why I'm doing it this way. The run is already there, so I'm going to use it instead of buying new. I think this covers just about everything.
 
TL;DR
Short run of 8 guage thhn on a 50a breaker. Good to go?
I have 6-6-6 triplex overhead that I'm running to a detached garage. At the weatherhead at the garage I'm going to splice 8 guage thhn copper to run down to the sub panel (approx 5' max of 8 guage at both ends of the run). This feeder will be on a 50a breaker.
Does anyone see any issues with this? Everywhere I've looked gives me different answers on the 50a, 8 guage part.
For reference, the 8 and 6 guage are 90°c, and the terminals on the breaker are of course 75°c. 8 guage will be in pvc from the weatherhead to inside the subpanel. Will have a drip loop. Detached garage will have a ground rod. The run already uses 8 guage at the main breaker end which is why I'm doing it this way. The run is already there, so I'm going to use it instead of buying new. I think this covers just about everything.
By definition of the NEC if you are feeding a sub panel then you must pull an equipment ground from the source of power to the sub panel. Then no ground rod is required. As far as the sizing of your conductors you are supposed to use the 75 degree Celsius chart not the 90 degree section. # 8 is fine for a 50 amp supply and I’m assuming that you are not having this inspected.
 
By definition of the NEC if you are feeding a sub panel then you must pull an equipment ground from the source of power to the sub panel. Then no ground rod is required. As far as the sizing of your conductors you are supposed to use the 75 degree Celsius chart not the 90 degree section. # 8 is fine for a 50 amp supply and I’m assuming that you are not having this inspected.
At the barn sub panel (where this feeder came from) the neutrals and grounds were bonded. What would be the issue with doing it that way again, considering it's been that way for over a decade without any issue in the barn? Pulling a separate ground overhead isn't something I can do because I can't climb ladders (leg braces), so if I can get away with not hiring someone then that's what I want to do. And no, this will not be inspected.
 
At the barn sub panel (where this feeder came from) the neutrals and grounds were bonded. What would be the issue with doing it that way again, considering it's been that way for over a decade without any issue in the barn? Pulling a separate ground overhead isn't something I can do because I can't climb ladders (leg braces), so if I can get away with not hiring someone then that's what I want to do. And no, this will not be inspected.
We are supposed to tell you the correct way of electrical and not cut corners. By doing this your way is against the NEC regulations. I cannot advise you any further.
 
We are supposed to tell you the correct way of electrical and not cut corners. By doing this your way is against the NEC regulations. I cannot advise you any further.
I understand completely. I was just trying to see if there was another way to ground the subpanel besides running a ground wire all that distance. So two ground rounds at the structure six feet apart wouldn't work or be acceptable?
 
I understand completely. I was just trying to see if there was another way to ground the subpanel besides running a ground wire all that distance. So two ground rounds at the structure six feet apart wouldn't work or be acceptable?
I’m saying it is not by code.
 
I’m saying it is not by code.
But if I had pulled a permit for this under the 2005 code, it would be perfectly acceptable and safe, and an ahj would pass it today. Weird how electrons behave differently depending what year it is.
All joking aside, thanks for your help and taking the time to answer some questions. I also understand that all your answers must conform to the NEC, and that you can't/won't deviate from that, and I respect that. Thank you again.
 
But if I had pulled a permit for this under the 2005 code, it would be perfectly acceptable and safe, and an ahj would pass it today. Weird how electrons behave differently depending what year it is.
All joking aside, thanks for your help and taking the time to answer some questions. I also understand that all your answers must conform to the NEC, and that you can't/won't deviate from that, and I respect that. Thank you again.
Good luck my friend
 

Reply to Overhead triplex feeder termination question in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446
I would like to ask advice on a breaker size. Back in 2001 I turned my garage into a woodworking shop with several 240v machines. To power them I...
Replies
2
Views
1K
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K
Was wondering if the gurus can critique and/or provide recommendations on my plan to install two sub-panels in a (50'x100') 5,000 sq ft steel...
Replies
2
Views
1K
Need some help please. Got a brain teaser for my first post. My pool pump motor cratered over 4th of July. It was working fine and started to...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock