Farmelectrics

-
Arms
Reaction score
520
Question an under floor heating/ cooling box reading 17amp on my clamp meter but the supply is from a 13amp plug now I no a fuse or mcb can take 1 1/2 times its load for a certain time not sure for how long but my question is why hasn't this took the 13amp fuse out
 
Question an under floor heating/ cooling box reading 17amp on my clamp meter but the supply is from a 13amp plug now I no a fuse or mcb can take 1 1/2 times its load for a certain time not sure for how long but my question is why hasn't this took the 13amp fuse out

Have a look at the time/current characteristics (appendix 3 in BS7671). I cant find any tables for a BS1363 fuse that you are looking for but to put it in perspective a 15A BS3036 fuse will take 5 minutes to blow with 30A running through it and would take days of continuous use (probably weeks... if at all) to blow with 20A running through it, so I cant see 17A troubling a 13A fuse too much. At a guess I would say a week of continuous use at 17A might blow it, but a few hours a day probably wont touch it!
 
Last edited:
Have a look at the time/current characteristics (appendix 3 in BS7671). I cant find any tables for a BS1363 fuse that you are looking for but to put it in perspective a 15A BS3036 fuse will take 5 minutes to blow with 30A running through it and would take days of continuous use (probably weeks... if at all) to blow with 20A running through it, so I cant see 17A troubling a 13A fuse too much. At a guess I would say a week of continuous use at 17A might blow it, but a few hours a day probably wont touch it!


BS1362 fuse.
 

Reply to Overload in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
489
Hi there I need your opinion on this one, I need to fix mat 18sqm (200w). Client instead of one mat bought 2 mats (12sqm)+(6sqm) one thermostat ...
Replies
7
Views
863
Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
441
Hi All Wondering if anyone can point me in the right direction regarding uk double sockets. Is there a reg or a British standard that...
Replies
10
Views
2K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
893

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock