Is a kettle class 1 or class 11 , couldnt get continuity reading but cable has cpc in it

AlSo extension seem class 11 but have cpc in them as well ?

So are they class 1 or 11 in your experience

Strange
 
Cheers for replying . Is 4 way extension leads class 1 as have earth or class 11 as have all insulated cover?

I think there class 11 but have an earth for appliances plugged in. Because gives you continuity result where class 11 wouldn't . Sorry of confusion is working here.
 
All extensions should be tested as class 1 as they could be used for class 1 items , think about it , as with 110 volt insulating transformers they are class one , and watch out for the home made extensions made with 2 core cable all kettles are class one if you cant get a reading it could be due to a buildup of scale on the element try moving the earth clamp backwards and forwards whilst attatched to the element
 
Hi, The way to tell if something is Class 1 or Class 2 is to look for the 'square box' symbol. If you see that symbol then it's Class 2, if not then you must treat it as a Class 1.

Extension leads should ALWAYS be made of 3 core cable, and will need testing for Earth Bond and Insulation. Most PAT Testers also have the facility to do a Polarity test as well.

When testing a kettle the best place to get a good earth is the element. If it's a solid base kettle then try putting a screwdriver onto the base and putting the clip onto that.

If your PAT Tester doesn't have a facility for testing extension leads (all the modern ones do) then another option is to carry out the earth and insulation tests on the kettle, then plug that into the end of the extension lead and do the same tests again. You might get a slightly higher earth bond reading, dependent on the length of the cable.

Hope this helps!

Tim
 
But when recording results of extension lead is it class 1 class11 ?

Always a class 1. Record the value you obtained for the earth bond test, and you can usually record the insulation test and Polarity as 'Pass' - you would expect a reading 'off the scale' for the insulation.
 
Aye earth bond is 0.00 on most items , IR >20M
Which is all good

But the test results don't asK for anything other than earth bond and ,IR


Its a horrible we job lol ,but cheers guys

What about ATM machines, could nt disconnect do I just write visual on at report?
 
Also there was s 3p oven rating 9.8kw on an isolated switch. Where does this rating stand? I just did a visual and stickered it ,am I wrong
 
Aye earth bond is 0.00 on most items

Thats surprising, doesnt sound right. We just had our PAT tester calibrated and on the earth bond for IEC leads out of about 30 leads everyone read 0.00ohms, so Ive sent it back.

Also as mentioned look for the 2 squares symbol, if its not there then test it as class 1...
 
Hi, The way to tell if something is Class 1 or Class 2 is to look for the 'square box' symbol. If you see that symbol then it's Class 2, if not then you must treat it as a Class 1.

Extension leads should ALWAYS be made of 3 core cable, and will need testing for Earth Bond and Insulation. Most PAT Testers also have the facility to do a Polarity test as well.

When testing a kettle the best place to get a good earth is the element. If it's a solid base kettle then try putting a screwdriver onto the base and putting the clip onto that.

If your PAT Tester doesn't have a facility for testing extension leads (all the modern ones do) then another option is to carry out the earth and insulation tests on the kettle, then plug that into the end of the extension lead and do the same tests again. You might get a slightly higher earth bond reading, dependent on the length of the cable.

Hope this helps!

Tim
and if theres no evidence of the double square logo....or your unsure/can`t confirm/not verefied that an item is either class 1 or 2.....then treat it as class 1...
 
if it was hard wired into an isolator I would not class it as portable. that's part of the fixed instalation.

Emm no its not, a fixed appliance comes under ISI&TEE formally PAT a fixed installation stops at the socket /FCU/DP isolator thats what is causing a lot of bother within PAT as guys who are PAT trained and not electricians are not authorised to go into FCUs and DP isolators so the urban myth of if it aint got a plug top on it you dont PAT test well thats just plain wrong if its electrical equipment no matter how its wired then it supposed to be PAT tested.

Just to add storage heaters , ovens, hoods, come under ISI&TEE
 
Emm no its not, a fixed appliance comes under ISI&TEE formally PAT a fixed installation stops at the socket /FCU/DP isolator thats what is causing a lot of bother within PAT as guys who are PAT trained and not electricians are not authorised to go into FCUs and DP isolators so the urban myth of if it aint got a plug top on it you dont PAT test well thats just plain wrong if its electrical equipment no matter how its wired then it supposed to be PAT tested.

Just to add storage heaters , ovens, hoods, come under ISI&TEE

Yes point taken and I don't disagree but as a PAT service it stops at the Plug for me. I'm happy to test hard wired items with my safeblock but not at normal rates!
 

Reply to Pat testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
482
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
686
I am a new PAT tester for a school, and I am stuck testing a plasma globe. It has a two core wire going to it, but no class 2 mark on the...
Replies
18
Views
2K
Hi All I’ve come across this heater Ariston Andris Lux Undersink Water Heater 2kW 10Ltr - Screwfix -...
Replies
14
Views
2K
What is best practice when unable to access a plug on a class 1 appliance. Specifically a washing machine in this instance. There is also no...
Replies
3
Views
760

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock