Discuss Periodic testing with the power on and all loads connected in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

oracle

-
Esteemed
Arms
Reaction score
413
I recently watched a tester and his mate do a periodic inspection and testing on a social housing dwelling without turning off the power or disconnecting any loads.
The Ze was measured without disconnecting the main earth conductor and Zs taken with the loads connected. They subtracted the dodgy Ze from the dodgy Zs and recorded these as the R1 R2's. No insulation resistance was measured and RCD was tested using the test button on it.
 
I recently watched a tester and his mate do a periodic inspection and testing on a social housing dwelling without turning off the power or disconnecting any loads.
The Ze was measured without disconnecting the main earth conductor and Zs taken with the loads connected. They subtracted the dodgy Ze from the dodgy Zs and recorded these as the R1 R2's. No insulation resistance was measured and RCD was tested using the test button on it.
What was the companies name? Bodge it and Scarper, yes I l know it's old
 
Could have been a limitation set by the client but I doubt it.

I have no issue with calculating R1+R2 but this practice would probably fall foul of safe working guidelines.
 
Essex I agree with you about calculations provided that the values used are valid. Ze without disconnecting the earth and Zs with the loads connected would not produce valid values
 
Problem with calculating R1+R2, is what is the point?
What purpose does it serve?
It’s like writing the date as Weds 29/08/2018.
Who’s going to look at the report and care that it was done on a Wednesday?
Measure the Ze, measure the Zs, if anyone wants to know what the Zs minus the Ze equals, let them do the calculation.
Don’t put a calculated value in a schedule for test results pretending that you conducted that test when you didn’t.
 
Last edited by a moderator:
I recently watched a tester and his mate do a periodic inspection and testing on a social housing dwelling without turning off the power or disconnecting any loads.
The Ze was measured without disconnecting the main earth conductor and Zs taken with the loads connected. They subtracted the dodgy Ze from the dodgy Zs and recorded these as the R1 R2's. No insulation resistance was measured and RCD was tested using the test button on it.
So you did less than even them then? ;)
 
Problem with calculating R1+R2, is what is the point?
What purpose does it serve?
It’s like writing the date as Weds 29/08/2018.
Who’s going to look at the report and care that it was done on a Wednesday?
Measure the Ze, measure the Zs, if anyone wants to know what the Zs minus the Ze equals, let them do the calculation.
Don’t put a calculated value in a schedule for test results pretending that you conducted that test when you didn’t.
I believe dead continuity tests serve no real purpose on an installation which is already energised. These tests are for verifying that it is safe to energise. Therefore a standard agreed limitation I have is that cpc continuity will be verified through live (Zs) testing. Even GN3 recognises the validity of this approach.

The only time I might use dead continuity tests for a periodic inspection would be R2 and not (R1+R2) tests - to verify that e.g. a Class I luminaire (which might be awkward to remove and replace) was indeed earthed.
 
The Ze was measured without disconnecting the main earth conductor and Zs taken with the loads connected.
If the Earthing conductor or the main protective bonding conductors are not disconnected to remove parallel paths then it is a Zs - not a Ze.

Not really sure what you mean about removing loads to Zs test.
 
This sounds like a classic job from my company. Sending apprentices around doing social housing, giving them 2 hours to test and do all remedials. 4 a day. If they send me on them I get 2 done a day with no remedials, which is the reason I rarely get sent to them.

For what it’s worth with the calculations I’ll Ze with main earth disconnected, R1+R2 and calculate the Zs with one live test at the end of line to confirm is near enough the calculated result.
 
This sounds like a classic job from my company. Sending apprentices around doing social housing, giving them 2 hours to test and do all remedials. 4 a day. If they send me on them I get 2 done a day with no remedials, which is the reason I rarely get sent to them.

For what it’s worth with the calculations I’ll Ze with main earth disconnected, R1+R2 and calculate the Zs with one live test at the end of line to confirm is near enough the calculated result.
Sounds like that's one class outfit you work for Chris. hope there is nobody else from your firm on the Forum.
 

Reply to Periodic testing with the power on and all loads connected in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
841
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi there thanks in advance for the help iam still learning but soon to sit my trade test, on the booth picture number four is a TPN isolator I...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock