matyii

To protect equipment eg motors, generators, against phase-phase fault, one uses a Negative Phase Sequence Relay. Appreciate if anyone can explain the working principle of the relay. Is it similar to normal over-current IDMT relay?
 
Whenever there is an imbalance in a circuit, the imbalanced currents will have a negative phase sequence component. A negative phase sequence (or phase imbalance) relay is often provided for the protection of generators and motors against imbalanced loading that may arise due to line-to-line faults. Such a relay has a filter circuit, which is responsive only to the negative sequence components. Since small magnitude over-current can cause dangerous conditions, it becomes necessary to have low settings on such relays. An earth relay can also provide the desired protection but only in cases when there is a fault between any line and earth. For line-to-line faults an earth relay cannot provide necessary protection and hence a negative phase sequence relay is required.
 

Reply to Phase-phase fault in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
599
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
616
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
956
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock