Discuss PIR code advice in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

E

eddie current

hi guys
im new here so please be gentle with me...lol
i have just started a new job in a factory, maintenance spark.
a few years ago the company had a PIR carried out and guess what, its my job to sort out all the faults,,,,,,,, happy days... not
my question is
they have been given a code 2 for the neutrals not being identified in the db baords.
they are identified, well they are all black and in a neutral bar...
any advice please guys on the easiest way around this, its very hard for me to turn the power off to these circuits as we run 24 / 7
 
hi guys
im new here so please be gentle with me...lol
i have just started a new job in a factory, maintenance spark.
a few years ago the company had a PIR carried out and guess what, its my job to sort out all the faults,,,,,,,, happy days... not
my question is
they have been given a code 2 for the neutrals not being identified in the db baords.
they are identified, well they are all black and in a neutral bar...
any advice please guys on the easiest way around this, its very hard for me to turn the power off to these circuits as we run 24 / 7

Are the neutrals numbered correctly?

Regarding turning equipment off, you need to sort out a schedule with the boss. If he wants the faults sorted he needs to comprimise....Aske him to do one fault per day. Give him an estimate on how long that fault is going to take to rectify, theres not much else you can do in this situation.
 
Out of hours working......bit of extra cash for you maybe.....

I dont think a code 2 is correct in this case TBH.

A code 2 warrants an unsatisfactory verdict on a PIR, can anyone honestly say that a neutral conductor out of sequence really warrants that. For me, no.
 
Last edited by a moderator:
Although identified by color, can you identify the circuits to which they belong?

Sounds like a code 4 to me

If your after a Reg id look at 514.1.2.
 
Although identified by color, can you identify the circuits to which they belong?

Sounds like a code 4 to me

If your after a Reg id look at 514.1.2.

Yes, always a code 4 for me too but if, in the inspector's opinion, the non-sequential neutrals posed a danger in that particular installation then you're stuck with a code 2.
 
they didnt really state incorrect sequence, just incorrectly marked, they were wired to the 16th edition and marked in black, i think this guy expects blue tape on all the neutrals however this would make all the L3 live blues very dangerous in my opinion
 
they didnt really state incorrect sequence, just incorrectly marked, they were wired to the 16th edition and marked in black, i think this guy expects blue tape on all the neutrals however this would make all the L3 live blues very dangerous in my opinion

How ridiculous, apply a '2 colours' sticker and the job's done!
 
Yes, always a code 4 for me too but if, in the inspector's opinion, the non-sequential neutrals posed a danger in that particular installation then you're stuck with a code 2.

Well what would the risk be in the installation in its present state and what potential risks may develop from the non compliance with 514.1.2.

I think the risk posed would be down to the competence of the person carrying out work.
 
i think it would be bloody dangerous to sleeve them blue. the installation was wired in the proper colours, and to interfere with this would cause confusion and possible danger of electrocution. do they want all the other original colours sleeved? aboslute madness IMO.
 
its a 16th edition installation NO BLUE Sleeving required Mixed Wire sticker on dbs If the neutrals don't correspond 1.1 2.2 ect then IMO its a code 4 and a lable on db stating non sequential neutrals
 
or 15 minutes swapping the conductors into the correct terminal numbers.
 
Would a fuse finder work on neutrals? I'm too lazy to try it but it might help identify neutrals without a shutdown. 'Course you might then need to re-arrange them in the block,
 
314.1 (ii) would be one

Hi , not sure how this means it mustb be sequential , i dont have book in front of me but googled the reg you quoted,
thanks

Regulation 314.1 Every installation shall be divided into circuits as necessary to avoid danger and inconvenience in the event of a fault,
take account of danger that may arise from the failure of a single circuit such as a lighting circuit, reduce the possibility of unwanted​
tripping of RCDs etc
 
Well you seemed to have quoted (iii) (i) and (iv) but the one I quoted was (ii)

Facilitate safe inspection, testing and maintenace (see also section 537).

IMO non sequencial neutrals does not aid any of those 3 things and could even be an hinderance to it. So unless I considered the neutrals to be particularly risk, I would code it a 4. Also as mentioned 514.1.2 is another IMO you could cite, I just did the first one off the top of my head, though in all honesty 514.1.2 is the better one to put on a PIR as it is more concise.
 
a bit of a grey area really then, i agree non sequential neutrals does not aid, . will look at 514 tomorrow when book is in front of me
.
cheers
 

Reply to PIR code advice in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
547
Hi guys I’m at one of the funny times in my career where I can’t decide on what I want to do. I’m wondering if one of you experiences folks can...
Replies
0
Views
192
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
423
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
794
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock