Discuss pir code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Farmelectrics

-
Arms
Reaction score
520
just carried out a pir on 3 bedroom semi hager split phase board rewired 2000 the instalation is of a good standard and all readings comply with bs7671 few problems found were 3 bedrooms upstairs all with brushed crome spots looked in loft neat job done with cabling all into lighting jbs but no earth to crome spots what code would you use for this was thinking of code 2 myself but looking to see what you guys think also in the garage which joins the house t&e cabling clipped direct to brick work before heading under floor boards am i being a bit fussy snagging this as there is no mechanical protection what code would you use for this or would you accept it
 
Yes think your right coding the class I fittings as a code 2. If the house was rewired in 2000 then I assume the cable would have a CPC in it, would it be much of a job to connect the CPC's up as a good will gesture.

On the T+E clipped direct, if you feel that it might be of risk of damage then yes you could code it, but if there is little chance of that then leave it.
 
yes malcom its t&e old colours think your right with garage will leave it gettin to keen suggesting putting it in plastic trunking etc will code spots a 2 and for a small charge will earth the spots good will dosnt pay bills lol
 
and some of the 230v spots are class II. i missed that on ist reading of the op.
 
some 230v spots are only 2 terminal. the lampholder is isolated from the metalwork of the fitting, so they are classII.
 
iv'e seen a lot with just 2 terminal block, but no double square, unless iv'e missed it. i just go by the 2 terminals. if there's no provision for terminating cpc to fitting then i just put the cpc in a 3A choc.block.
 
I hate fittings with only 2 terms even if the CPC isnt required there should still be provision to connect one even if just to keep continuity


I think it's not there for a reason, in case it confuses anyone. "This is a class II equipment and must NOT be earthed" are words you'll come across. Separate 3A chocolate block should save the day. Cheers
 
Even if the fittings are class II there still should be an earth at the point of termination as per reg 412.2.3.2, so if as the OP said they have been cut off, then it would be a code 4 for the class II fittings, and of course the original code 2 if class I
 

Reply to pir code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
837
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
953
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi all, we have a much discussed topic. Swa and the earthing of the amounting through a fly lead. What your thoughts and how would you code an Swa...
Replies
4
Views
3K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
625

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock