- Reaction score
- 356
Morning all...
Done PIR yesterday all pretty good.
Just one issue want to see what you chaps think:
'Cooker supply fed on 32a 6mm supply to isolator located in cupboard next to cooker, less than 2m away. Also fed off load of isolator was the supply for the hob ignitor.'
I'm sure the isolator in the cupboard will be ok, because under 2m away. But not so sure about hob ignitor, normally would have put this on a FCU ?
Any thoughts please??
Many Thanks,
Sy
Done PIR yesterday all pretty good.
Just one issue want to see what you chaps think:
'Cooker supply fed on 32a 6mm supply to isolator located in cupboard next to cooker, less than 2m away. Also fed off load of isolator was the supply for the hob ignitor.'
I'm sure the isolator in the cupboard will be ok, because under 2m away. But not so sure about hob ignitor, normally would have put this on a FCU ?
Any thoughts please??
Many Thanks,
Sy