Discuss PIR..... thoughts on this please....? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

sythai

-
Arms
Reaction score
356
Morning all...

Done PIR yesterday all pretty good.

Just one issue want to see what you chaps think:

'Cooker supply fed on 32a 6mm supply to isolator located in cupboard next to cooker, less than 2m away. Also fed off load of isolator was the supply for the hob ignitor.'

I'm sure the isolator in the cupboard will be ok, because under 2m away. But not so sure about hob ignitor, normally would have put this on a FCU ?

Any thoughts please??

Many Thanks,

Sy
 
Considerr the current carrying capacity of the igniter load cable...

The original manufacturers instruction would have stated the fuse rating I would gave thought? You may be able to research them online or something. So you'll have the code for the CCC and another code possibly for failing to install fixed equipment to the manufacturers info as BS7671 2008 requires.
 

Reply to PIR..... thoughts on this please....? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
706
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
806

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock