Discuss Plastic board above entrance with bs1361 fuses only - no RCD protection. How would you code that? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The fact that the board is plastic and above the entrance. Also i am a bit confused about those old type 1361 fuses with no RCD. Now if we agree with the cx. that i need to fit RCD, is it good idea to fit RCD in cooperation with the existing fuses or i need to replace the whole board ?What observation are you making that you want help to code?
No outdoor sockets or equipment.For the board itself - no code as looks to be in good condition and no signs of thermal stress, etc.
As for the lack of RCD, that would normally be C3 assuming no outdoor (or likely feeding outdoor) sockets and if the bathroom has supplementary bonding as per regs of the time. Otherwise C2.
Good guidance in the Best Practice Guide #4 free from here:
Best Practice Guides | Electrical Safety First
Electrical Safety First produces, in association with other industry bodies, a range of Best Practice Guides which provide definitive information and guidance on a range of technical subjects.www.electricalsafetyfirst.org.uk
In particular the entries on pages 14 and 16.
The fact that the board is plastic and above the entrance. Also i am a bit confused about those old type 1361 fuses with no RCD. Now if we agree with the cx. that i need to fit RCD, is it good idea to fit RCD in cooperation with the existing fuses or i need to replace the whole board ?
As I say I would code the board a C3. Regarding the bs1361 fuses, provided the efli values are ok and meet the fault protection requirements and disconnection times they are fine.The fact that the board is plastic and above the entrance. Also i am a bit confused about those old type 1361 fuses with no RCD. Now if we agree with the cx. that i need to fit RCD, is it good idea to fit RCD in cooperation with the existing fuses or i need to replace the whole board ?
How tall is the block of flats? Is it a HRRB? Does it require AFDD’s
4 floors highHow tall is the block of flats? Is it a HRRB? Does it require AFDD’s under amendment 2?
Thanks mate, helpful info!As I say I would code the board a C3. Regarding the bs1361 fuses, provided the efli values are ok and meet the fault protection requirements and disconnection times they are fine.
With respect to rcd protection. If there is supplementary bonding present in the bathroom then C3.
If the use of mobile equipment outdoors can’t be plugged in and used C3.
Otherwise both the above would be C2 if the there is no supplementary bonding and outdoor equipment can be plugged and used outside.
Things like for example cables embedded within the walls at a depth not greater than 50mm would warrant a C3 unless the cables are appropriately protected, as when the wiring system was installed it may have complied with the current edition of bs7671. Without personally carrying out the test though it is difficult to code. As the tester you may identify certain risks within the installation that may warrant a C2.
If they wanted the board changing and rcd protection installing then I’d change the DB for a metal rcd/spd board. Hope that makes sense. I’m sure someone will pull me if I’ve missed something.
If you are installing new circuits or replacing a db in a HRRB…yes an afdd shall be installed.
I believe on an eicr it would be a C3.
Yes agree. If you are adding a socket then you need to comply with the current regs.Even if adding a socket you’d need to too.
I agree with a C3 on an EICR, but I’d make a note recommending them.
What does the DNO equipment look like. For instance does it have any RCCB or even RCD at the supply end. I assume this is a sub-main. How does the supply get to that CU?
So I am guessing there is no ryefield or main plant cupboard that one meter does the flat direct does it? Is that how all the flats are fed each with their own cut-out? Unusual.
Reply to Plastic board above entrance with bs1361 fuses only - no RCD protection. How would you code that? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net