Table 53.4 shows that plugs and unswitched socket outlets can be used as devices for isolation while carrying load current!. Functional switching can also be carried out in this way as well. Is this really a safe procedure?
Am I interpreting this table incorrectly.

Thanks

Jonel
 
If it wasn't a safe procedure then 13amp plugs / sockets would be interlocked so you can't unplug until they're switched off.
Just as a lot of larger plug / sockets are.

Any arc drawn from the pins will be contained within the socket.
To my knowledge it's not been a problem in the last 50 years.
 
Folks perhaps feel safer using a switch to isolate (especially if something odd is going on with the appliance) but pulling the plug definitely does the job.
 
Thanks all. If it's unplugged it's isolated! I have no problem with that. My question was about when load current was still being drawn. That has been explained, thanks. I do understand, and the regulation did say it, it just bothered me a bit. Pulling out plugs while they are carrying a load somehow did not feel right.
I'm happy that I was interpreting the Table correctly. Also pleased the very prompt response from very knowledgeable electricians.

Thanks again
 
Using a plug & socket for isolation is within regulations and perfectly safe. You may be confusing emergency switching with isolation, as explained below:

Isolation:
- Without mentioning all points, it specifically mentions that all live conductors must be disconnected (live meaning - carrying current under normal circumstances, such as line & neutral)
- Once isolated, there is no risk of electric-shock.

Emergency-Switching
- Emergency switching, capable of switching full-load current (often marked red, such as the CU main switch).
- It's good practice to unload a CU before turning-off the main switch, but not actually necessary.
 

Reply to plugs and unswitched socket outlets used as isolators! in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Hi there, I have two isolation switches above a kitchen workcounter. They currently turn off the power to a pair of unswitched sockets which are...
Replies
2
Views
3K
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
214
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
782

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock