Discuss Pme TT in same farm building in the UK Electrical Forum area at ElectriciansForums.net

Rkidcd

-
Reaction score
2
Metal farm building currently has single phase TT supply with all the required bonding in place.

Client requires a 3 phase supply for a piece of equipment in this building - is it possible to bring a 3 phase supply from the farms house which is PME?
 
That is a high risk strategy considering TN-C-S is not permitted in farm buildings.
 
Sorry I should have said it's a storage building not used for livestock. Anybody got any ideas to a solution?
Doesn't matter. There is a high shock risk should you introduce a derived earth into a true earth (TT) environment. Why can't you TT it?
 
Sorry to bring this back up but I would like thoughts on my plan based on the above advise.

I'm going to bring 3phase PME supply across from main building to metal outbuilding but isolate the earth externally.

This means that I'll be TTing this new supply but what I need advise on is whether I sink a new Rod for this or would it be possible to use the Rod already installed for the current single phase TT supply the building uses (see original post for background info)

Thanks in advance
 
So long as the single phase supply is coming from the same supply transformer then you can use the existing earthing method. If the three phase supply and the single phase supply are from different transformers then you would be providing an earth link between supply transformers which could be a very bad idea. Circulating currents, and possibilities of transferring faults to other systems spring to mind.
 
If the supply cables are overhead follow them to see where they come from; if the single phase supply is from the same service head as the three phase supply they are the same;start with the basics and if there is no luck there then contact the DNO and hope.
You also need to consider the effects if there are two different supplies in the same building, but find out where they are fed from first.
 
That is a high risk strategy considering TN-C-S is not permitted in farm buildings.

Pme is allowed if there is a metal earthing grid embedded in the sgreed with multiple earth connection points.

That said i love TT and loath exporting pme.. cant you do away with the single phase supply and upgrade 3 phase into whole building and TT it?
 
Sorry to bring this back up but I would like thoughts on my plan based on the above advise.

I'm going to bring 3phase PME supply across from main building to metal outbuilding but isolate the earth externally.

This means that I'll be TTing this new supply but what I need advise on is whether I sink a new Rod for this or would it be possible to use the Rod already installed for the current single phase TT supply the building uses (see original post for background info)

Thanks in advance

its possible to use the existing electrode if you have confirmed that it is suitable for the job.
I'd probably look at augmenting it with additional new electrodes if possible to get the best earthing connection possible
 
You'll need to consider what to do about having the two different earthing systems in installation and so be no further forwards.

As both earthing systems would be TT is the risk not sufficiently reduced? (as apposed to a TT earth and PME earth)

If not it sounds like I either:

1.confirm both supplies are from same source and use one TT earthing system (possibly using multiple rods)

2.get rid of single phase supply and supply entire building from the new 3 phase PME supply (with TT earthing)
 
Visited site again today and it isn't really practical to lose the existing single phase TT supply so it's looking like option 1

Any more thoughts on the issue?
 

Reply to Pme TT in same farm building in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
523
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread). At present the farm is all PME. I believe it needs...
Replies
9
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
557
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock