Discuss Possible Job For Tomorrow in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
Reported as occasional trip of an RCD. Leakage current noted 2.5A when cooker switched on (which is on a 30mA RCD). Could be interesting.
 

Attachments

  • Photo0118.jpg
    199.4 KB · Views: 235
If the cooker is on and it's leaking >30mA why has it not tripped then?

2,500,000 / 1000 gives milliamps

mA = 2500mA

IR = 230 / 2500

IR = 0.092 Ohms

if I'm correct in my calculation you have a almost a dead short somewhere? Either this is correct or I'm going to look like a right plonker.

working it the other way just to check...

R = IR x 1,000,000

R = 92,000

I = 230 / R

mA Leakage = I x 1000

mA = 2.5A
 
The 'occasional trip' and the 2.5A leakage current don't really go well together. 'Won't reset' would be better.
Measuring the leakage down the CPC or main earth doesn't show you what's being lost down parallel paths so it's not the most accurate way of testing..
 
The 'occasional trip' and the 2.5A leakage current don't really go well together. 'Won't reset' would be better.
Measuring the leakage down the CPC or main earth doesn't show you what's being lost down parallel paths so it's not the most accurate way of testing..

I can't see how the RCD would hold if it 'is' leaking that much.
 
Are you asking for hints/tips or just informing us of your working day ahead?

It has got me thinking and cannot work on it further until landlord gives permission. Thought it might give a few of you a puzzle to think about on your sunny Sunday afternoon. I am puzzled as to why the RCD has not tripped because outwardly it looks like a Neutral Earth fault, but I have not checked yet to find out more specifically where the the problem is. The lighting and smokes are not on the RCD. Also as someone, has mentioned here already, the occasional RCD trip could be unrelated to this high residual current. Hopefully I'll get the job and will be able to satisfy my curiosity.
 
The Rcd is faulty and there is a dodgy ring on the hob, test the rcd as per usual, at times half, one and five on 0 and 180 degrees, that will sort that bit out, then you can look at whats going on with the oven.
 
If the cooker is on and it's leaking >30mA why has it not tripped then?

2,500,000 / 1000 gives milliamps Leave I in Amps, not Milliamps

A = 2.50A

IR = 230 / 2.50

IR = 92 Ohms

if I'm correct in my calculation you have a almost a dead short somewhere?
Not a dead short at 92 Ohms
 

Reply to Possible Job For Tomorrow in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Whats everyone's take on this, turned up today to start a re-wire and yet again there wasn't any toilet on the job so we ring the builder and he...
Replies
75
Views
6K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
709
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
884
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
818

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock