Discuss Potential Overloaded? (Kitchen Oven & Hob) in the DIY Electrical Advice area at ElectriciansForums.net

Cupa

-
DIY
Reaction score
7
Popped round my old dear's yesterday. She quite fancies replacing her ceramic hob with an induction one, so I thought I'd take the oven and existing hob out to see what state the wiring is in (property built 1930s although I expect probably had a refurb at some point in the 70s or 80s, but nothing since).

Anyway, pics attached of what greeted me. The oven & hob are both wired to a single cooker outlet plate, with a cable going back to a 32a breaker on the consumer unit.

Issue I have is that the hob is 2.8kW & oven is 6.6kW (9.4kW). Based on a 32a breaker x 230v = 7.4kW. So that little combo there is 28% over the breaker rating.

However, I think the reason why the CU doesn't kick in is because the old dear hardly ever uses both hob & oven on full whack.

Anyway, my question is, setting aside theory and regs for a sec, in the real world what I found, how much of a potential issue is this?

I'm also itching to change the cooker outlet plate to a nice modern one (I have lying about as a spare).

AAA.jpg

BBB.jpg
 
Right, I am a mere novice and know sod all about anything but will have a go. Let me know where I am wrong, haha!

So, we have the following connected loads - a 2.8kW hob + 6.6kW oven = 9.4kW = 9,400, divide by 230v = 40.87.

Unless I am a complete muppet, I read that for a cooker the diversity applicable is 10a + 30% balance?

Based on that you calculate 30 x (40.87 - 10) / 100 = 9.26.

So 10a + 9.26 = 19.26 + allowance for socket outlet of 5 = 24.26?

I probably got that wrong as I have both an oven and a hob together - do I need to do a calc for each instead of joint?
 
You might find the JW youtube vid helpful...

From about 12min onwards... worked example
 
Right, I am a mere novice and know sod all about anything but will have a go. Let me know where I am wrong, haha!

So, we have the following connected loads - a 2.8kW hob + 6.6kW oven = 9.4kW = 9,400, divide by 230v = 40.87.

Unless I am a complete muppet, I read that for a cooker the diversity applicable is 10a + 30% balance?

Based on that you calculate 30 x (40.87 - 10) / 100 = 9.26.

So 10a + 9.26 = 19.26 + allowance for socket outlet of 5 = 24.26?

I probably got that wrong as I have both an oven and a hob together - do I need to do a calc for each instead of joint?

Looks right to me, so a 32A circuit is correct for this combination of appliances.
The method of connection to the cooler plate is less than ideal though.
 
I have one of these left as a spare (45a cooker outlet plate), and while it can probably accommodate dual inputs, it is not designed as such I don't think.

Induction-hob-plate.jpg
 
It’s not designed for dual output. If you think about it you’ll have 3x6mm cables in each terminal. And they aren’t made for that.
This what you need

The existing circuit at 32A is fine for what you plan to connect to it.
While you are at it, PLEASE put some grommets in the holes of that back box!
 
Although not required does this have a double pole control switch or just come straight from CU.

Helps if cooker or hob ever develop a N-E fault and can be isolated at the switch to avoid any RCD split load tripping issues.
 
Thanks to all, I'll pop down to TLC and grab one of those. I have some spare grommets, of course, I will whack one on. I was surprised myself when I took the cover off and saw no grommet!

Form what I can tell, the cable goes from the CU to a Schneider cooker switch (double pole), and from there to the cooker outlet plate.

Thanks to all by the way, appreciate you taking the time to reply to me. I am learning new stuff all the time! :)
 
Thanks to all, I'll pop down to TLC and grab one of those. I have some spare grommets, of course, I will whack one on. I was surprised myself when I took the cover off and saw no grommet!

Form what I can tell, the cable goes from the CU to a Schneider cooker switch (double pole), and from there to the cooker outlet plate.

Thanks to all by the way, appreciate you taking the time to reply to me. I am learning new stuff all the time! :)
every day's a schoolday.

 

Reply to Potential Overloaded? (Kitchen Oven & Hob) in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K
Hi Guys, I am just changing my plug top oven over & gas hob and noticed the following: 32AMP Breaker > 6MM Cable > Cooker Switch 45a > 4mm cable...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock