Hi guys,

please bear in mind I'm not a pro with this.

i am trying to replace the G4 halogen capsule in my two ceiling fittings. These are brand new identical fittings and each has 7 20w halogens. I have replaced these with 2w led G4 capsules. Now this is my problem, birth lights are powered at the same 1 way switch, light 1 has all the bulbs lit no bother, for some reason the second light only has three of the bulbs lit very dimly. Is there an explanation for this ?

regards

justin.
 
G4 lamps run at 12V and for halogen lamps are supplied by a transformer that provides 12V a.c.
LED lamps are intended to work on 12V d.c. and are usually supplied by a driver (a power supply as opposed to just a transformer).

Most 230V to 12V transformers have a minimum wattage at which they can operate (often around 10W) you are fitting 14W of lighting when using the LEDs, it is possible that there is a slight variation in the capabilities of the transformers in the fittings or possibly in the actual power consumption of the LED bulbs (you could check this by changing all the bulbs to the opposite fittings and see if it changes, if you can be bothered) and that this variance means one transformer can just cope with the minimum load and the other one is just under the minimum load.
The one just under minimum load cannot transform the power effectively and will be dim.
If you put one halogen bulb in the fitting along with the six LEDs it should work all lamps correctly.

Ideally you should see if you can obtain, say, 20W LED drivers that can fit in the fitting in place of the existing transformers, this will extend the life of the LED bulbs and they should be able to cope with almost 0W loads.
 
Wow, very concise explanation, thanks and makes sense now as I did put one halogen in and all worked as you describe. I'll pop into a wholesaler this morning and see what they have in the way of drivers.
 

Reply to Problems with LED bulbs in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
505
I purchased a house that has a really cool 12v halogen setup where two wires are suspended across the ceiling in two different locations, and each...
Replies
9
Views
923
Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K
I have a street light circuit on land I rent out. I need to replace 2 of the bulbs. 1 of them is an old Philips 55W SOX Plus, the other is a...
Replies
3
Views
553

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock