Discuss problems with test results in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
-8
Hello,

Im confused as to why I'm getting a high zs value at the socket but all r1 rn r2

ze is 0.5 but zs is .98

The other problem is a had a rcd won't trip but for some reason when something is plugged in it trips the other rcd.

All circuits bell out and test fine so could it be the rcd that is playing games with me ?
 
RCDs don't play games, they react to a current imbalance. The symptoms you have described are of a reasonably common fault and a bit of logical thought and application of your knowledge of the fiends of electricity should make it clear.
You almost certainly have a N-E earth fault.

I don't see what the problem with your Zs reading is??
 
Hello,

Im confused as to why I'm getting a high zs value at the socket but all r1 rn r2

ze is 0.5 but zs is .98

The other problem is a had a rcd won't trip but for some reason when something is plugged in it trips the other rcd.

All circuits bell out and test fine so could it be the rcd that is playing games with me ?
What was the R1+R2 reading?
 
You said that the Ze is 0.5
Im guessing its a tns & not tncs then as its over the 0.35 Ze max



If using 2.5 (1.5) T&E

Zs 0.98 - Ze 0.5 = 0.48

4 ÷ (2.5 + 1.5) x 0.48 = 0.3

r2 = 0.3 ohms
r1 = 0.18

Roughly lol, Am i close?
 
Had this two weeks ago in a fire damaged bungalow. I know it sounds implausible to some but a neutral to earth fault on a circuit stopped the RCD from tripping and test button wouldn't work. Dissed circuit in question...RCD now tests fine and test button works.
 
You will more than likely get a higher Zs through an RCD due to it's own resistance and also the test meter puts out a lower current on the no trip setting so the result isn't as accurate.
 

Reply to problems with test results in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
289
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
899
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock