I have recently had test readings as follows -
On a Fluke tester - loop test L/PE earth fault current 22.8 ohms but the loop test L/N was 0.14 ohms.
This points to poor main earth connection.

Should I report to DNO.

Have done in the past and after calling to test. They only test L/N and advise ok but direct Zs at light point fails with high reading.

Any help with this please.
 
Your results for a TNS are understandable, you have an adequate neutral path hence your PSCC is fine, but you are correct in your assumption that the main earthing is not well hence the crap PEFC and Ze.

Get the DNO out to fix it.

Cheers…………….Howard
 
http://www.electriciansforums.co.uk...cal-installations/9138-high-ze-value-tns.html

Read this 5yrs old but still has many valid points for you to consider and will save a drawn out thread..

Did you read that link before posting?? Right couple of charlies on there!! NOT exactly good advice to pass on when one, is just submitting to installing a TT system instead of insisting that the DNO provided a PME connection in accordance with the satutory duty to maintain a provided DNO earth!! lol!!
 

Reply to Prospective fault current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
Replies
12
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
862
hi, new to this forum and still training. During testing for prospective fault current at the point I get a bad reading, what ever that may...
Replies
3
Views
1K
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock