I have recently had test readings as follows -
On a Fluke tester - loop test L/PE earth fault current 22.8 ohms but the loop test L/N was 0.14 ohms.
This points to poor main earth connection.
Should I report to DNO.
Have done in the past and after calling to test. They only test L/N and advise ok but direct Zs at light point fails with high reading.
Any help with this please.
On a Fluke tester - loop test L/PE earth fault current 22.8 ohms but the loop test L/N was 0.14 ohms.
This points to poor main earth connection.
Should I report to DNO.
Have done in the past and after calling to test. They only test L/N and advise ok but direct Zs at light point fails with high reading.
Any help with this please.