Discuss Protecting a boiler with a relay in the Central Heating Systems area at ElectriciansForums.net

Reaction score
1
I am fitting a Heat only boiler that just serves the radiator circuit, the boiler has its own dedicated block terminal connector on the PCB but I cannot connect the pump to it as we normally do, the pump is a commercial type and Worcester Bosch have stated it will damage the PCB because of the excessive load/current drawn by the pump.


W-B have advised fitting a relay to protect the boiler electronics. A work colleague has emailed me a picture (see link below) of one a sparky wired for him in similar circumstances but that's where the fun begins, can anyone please help me with a simple wiring schematic on how to install this particular relay to serve both pump/boiler and the other items listed below which may or not be relevant in relation to the relay


Other items fitted which may be relevant:


Honeywell RF2 Pack 1 RF Programmer and room stat

Honeywell T4360 Frost Thermostat

Honeywell L641B Pipe Thermostat

Relay image link: dav - https://ibb.co/nLwAUb

Thanks in advance for any help


Ps. I'm hoping it’s just a simple case of some knowledgeable soul identifying the Supply & Load side of the relay!
 
A1 and A2 are the coil. then 1 switches to 2, 3-4, 5-6, 7-8
 
The top is power in, the bottom is power out.
A1 and A2 are for your control wires the rest are for what you want switched.

Thank you both for the swift replies. As you are aware I am not a sparky, I do however have knowledge of heating controls, but both anwers are confusing me a little, can either of you chaps post me a visual link of a wiring diagram as I can understand this better, sorry to be a pain :/
 
Basically, the cable that you would normally take from the boiler control to the pump goes instead to contacts A1 and A2. Brown in A1 and Blue in A2.
You then take power to the the other terminals on the contactor.
It’s preferable to take this power from the same source as supplies the boiler, but that may be impractical?
Connect Brown to terminal 1 and Blue to terminal 3.
From the bottom of the contactor you take power to the pump. Brown in terminal 2 and Blue in terminal 4.
I would then connect all the Earth wires together using a terminal block.
 
Slightly the connections are correct the discription is in error. What you have is an electricly controlled switch. When power is put onto terminals A1 A2 this causes a coil of wire inside to become a big magnet and thus the insides of the switch move. If A1 A2 were a CONTACT and not a COIL then it would short stuff out, big bang and a repair bill.

As stated above wire A1 A2 to the boiler in place of the pump and all should be good.
 
Basically, the cable that you would normally take from the boiler control to the pump goes instead to contacts A1 and A2. Brown in A1 and Blue in A2.
You then take power to the the other terminals on the contactor.
It’s preferable to take this power from the same source as supplies the boiler, but that may be impractical?
Connect Brown to terminal 1 and Blue to terminal 3.
From the bottom of the contactor you take power to the pump. Brown in terminal 2 and Blue in terminal 4.
I would then connect all the Earth wires together using a terminal block.


Apologies but can you just clarify, A1 & A2 are permant live & neutral from the breaker? I think i understand the rest of your guide
 
Get the wiring diagram for the boiler, identify the pump on the diagram for the boiler, connect A1 A2 where the pump is shown the on the wiring diagram for the boiler. Connect the rest as stated above
 
Basically, the cable that you would normally take from the boiler control to the pump goes instead to contacts A1 and A2. Brown in A1 and Blue in A2.
You then take power to the the other terminals on the contactor.
It’s preferable to take this power from the same source as supplies the boiler, but that may be impractical?
Connect Brown to terminal 1 and Blue to terminal 3.
From the bottom of the contactor you take power to the pump. Brown in terminal 2 and Blue in terminal 4.
I would then connect all the Earth wires together using a terminal block.

Also thank you too Spinlondon for taking the time and trouble to help
 
Get the wiring diagram for the boiler, identify the pump on the diagram for the boiler, connect A1 A2 where the pump is shown the on the wiring diagram for the boiler. Connect the rest as stated above

Update

To UKMeterman and spinlondon repectively, I have attched a basic wiring diagram below that I created in Microsoft Paint, can either of you please tell me if I have interperated your wiring guide incorporatiing the 'Contactor' switch correctly?

Thanks

Link: PROPOSED PUMP WIRING DIAGRAM - https://ibb.co/jUGgpb
 

Reply to Protecting a boiler with a relay in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

It has become a common occurrence that my boiler is failing to respond when the thermostat kicks in. I hear an audible click from the heatlink...
Replies
16
Views
2K
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
447
At our church, one of the things I've done is sort out the heating wiring (as best I can for now). The schematic is as shown below. The theory...
Replies
2
Views
2K
Hi Guys, Does anyone have any tips on wiring a boiler with mid position valve. I've been rewiring a house and have had the job of wiring the...
Replies
3
Views
4K
L
Hi all, I am trying to change my honeywell analog thermostat with a wireless thermostat . My current thermostat is T6360 Room Thermostat -...
Replies
13
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock