Got a 200m run of 3 core 10mm swa to install in a trench. Rather than pulling it through a duct, was wondering if anyone has ever pulled the duct over the cable, then dropped in into trench.
Duct is 50mm internal diameter flexible type. Might be a non starter, just weighing up options.
Thanks for any help.
 
Good evening all
Got a 200m run of 3 core 10mm swa to install in a trench. Rather than pulling it through a duct, was wondering if anyone has ever pulled the duct over the cable, then dropped in into trench.
Duct is 50mm internal diameter flexible type. Might be a non starter, just weighing up options.
Thanks for any help.
50mm = 2 inches 10mm SWA 3 Core gonna be tight hope you have a strong pull cord good luck, same as what cliffed said, in complete agreement with him
 
I'd say non starter, unless you did it with several men / women / others, to lift the weight.
50 mtrs of SWA weighs around 40kg so when you're dragging the 50mtr length of duct you've got 40kg of SWA bearing down on it once you get a full length of duct on the cable.

At best you'll rip the duct, defeating the whole purpose of using it.
 
But on another note I either wouldn't install a duct unless requested my client or 4 inch duct. Wouldn't bother with 50mm it'll be a nightmare
 
If you already have bought the duct and it is not reusable/returnable then you might as well put it over the SWA before dropping it in. But 200m is a long pull no matter what, though a team of heavies and plenty of cable lube might allow it but really you ought to be looking at something bigger.

If you do decide just to put the cable in the ground directly then make sure you have 5-10cm of sand down first, and the same on top afterwards, to stop stones and other stuff from damaging it as you back-fill.
 
save all the hard work. hire Mighty Mole for a day.
1620461347244.png
 
If pulling a 200m length of duct over a 200m length of SWA with a 200m pull cord you need 400m of space in a straight line to do it, and that is only if the draw cord is already in the duct, I did this with an alarm cable, but only 100m, would be easier in 50m sections with draw pits.
 

Reply to Pulling in swa in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
708
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
420
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
551
When putting in some duct for fibre broadband we also put in a few lengths of 63/50mm twinwall duct "just in case" we needed that, as we knew of a...
Replies
9
Views
1K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
893

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock