And the sand wont be cheap! 200m at 200mm thick (100mm below cable and 100mm over the top) and say 200mm wide trench = 8cu m (8 builder bags worth)!It is an expensive cable
Single socket maybe?Just being nebby but what's it feeding?
Well 5% drop and 10mm single phase comes to 12.3A over 200m so not far off it!Single socket maybe?
Doubt it could be that, I just did a quick VD calc and 5% is exceeded at a load of 13A over that distance for 10sqmmSingle socket maybe?
Well 5% drop and 10mm single phase comes to 12.3A over 200m so not far off it!
~12A is a lot of LED illumination!I calculated 7.54v at 13A over 200m but at 12.3A it could be slightly under 5%
but either way certainly nowhere near 3% for lighting!