Discuss Pulling SWA through a moled hole. in the UK Electrical Forum area at ElectriciansForums.net

gazj82

-
Reaction score
132
Guy from a company we have done a lots of work for over ther years asked me the following today and I didn't really have a good answer since all SWA I have ever had any involvement in installing has always been through a dug trench.

"What are the implications of pulling a SWA through a hole moled through the ground, do we need to duct it first? Will the cable stretch if pulled through directly, i.e with the resistance / friction of earth against its sheath. Is this likely to damage the sheath."

I couldn't really give him a answer I was sure on, hence why I am asking here.

I haven't actually worked out the cable size yet, in fact he hasn't even sent through the Building spec yet for me to determine the size of supply needed.

At a guess on what he has told me for the buildings nature, it will at least be 4 core 25mm pulled through 160m of earth.

What are your thoughts on drag this through the ground with a mole. Would you like to see a duct pulled through first?

I would be worried about a something sharp in the ground binding and damaging the cable, even though according to him they do have some sort of lubricant the mole pulls through first.

Thanks Guys
 
How will you get the warning tape on, and I would be worried about sharp stones . I have never done this, although I have seen them go under the main road and burst the main supply cable at the other side lol.
 
It's gonna be a cow of a pull through 160m in one go.

All of your thoughts about stretching, rough ground and snagging are worries.
How the heck do you install your warning tape as well ???
 
If you hit and damage other services £100 a day will be a bargain, probably quicker too, time you dig the pits by hand ;
 
The cable will be stretched to buggery, as the only way you'll be able to pull it in will be with a tractor or the like!! Forget all about it, it's a fools errand!!
 
His clients site is in the middle of London, they have existing buildings all over and nothing but roadways in between.
He has done it before (so he should know more about it than me!) for them on one of his much bigger projects (that one was too big for me), but he was pulling in 240mm (from his memory) and I know if anything it was further than 160m on that occasion.

I have no idea how he markered it last time, but I do believe they pulled it very deep below all other services in the roadways. Knowing him and his client, Exactly where it is will be heavily documented although no amount of paperwork makes up for no marker imho

The moleing machine pulles it in at a nice slow rate afaik Engineer54, has a camera on it and everything. There is no way anyone would be doing it with a tractor!

The last building he did the M+E was a few million though, it might not be in the budget this time - and it's a temporary building, will be there a few years at most!
 
The mole pllough will feed the cable in as it drives along
but you will not be able to fit the tape half way up
see you tube for video of pipe being pulled in
 
Last edited:
Bloody hell. Do you have any idea what's below the streets of London? - talk about a minefield.

Using a moling machine would be a bit like walking through a area filled with land mines.
 
we pulled a 240 and 300 swa in an open trench at yeovil sewage works used a ford transit van to tow them
the cable stretched and every time i glanded the ends the sheith crept back
 
we pulled a 240 and 300 swa in an open trench at yeovil sewage works used a ford transit van to tow them
the cable stretched and every time i glanded the ends the sheith crept back

Did you replace the stretched cable? Daz
 
His clients site is in the middle of London, they have existing buildings all over and nothing but roadways in between.
He has done it before (so he should know more about it than me!) for them on one of his much bigger projects (that one was too big for me), but he was pulling in 240mm (from his memory) and I know if anything it was further than 160m on that occasion.

I have no idea how he markered it last time, but I do believe they pulled it very deep below all other services in the roadways. Knowing him and his client, Exactly where it is will be heavily documented although no amount of paperwork makes up for no marker imho

The moleing machine pulles it in at a nice slow rate afaik Engineer54, has a camera on it and everything. There is no way anyone would be doing it with a tractor!

The last building he did the M+E was a few million though, it might not be in the budget this time - and it's a temporary building, will be there a few years at most!


Now forgive me if i'm wrong, but you did say ..... "What are the implications of pulling a SWA through a hole moled through the ground, do we need to duct it first? Will the cable stretch if pulled through directly, i.e with the resistance / friction of earth against its sheath. Is this likely to damage the sheath.".... You didn't state at any time that the mole was pulling the cable!!!!

Never used a mole to pull a cable direct, it's always been to pull a duct and draw line ready for a cable, and then only over short spans. I've yet to see a mole pull in a 3 or 4 core 240mm SWA cable over a 160 metres. Not saying it can't or isn't done, just that i have never seen or heard of it. It'll need to be one powerful mole machine to drag that sort of weight behind it, and i wouldn't like to give any odds on there not being any sheath damage either!!
 
Sorry for misleading you Engineer54 - it's hard to remember every detail when posting a new thread. The to and thro questions and answers don't flow like a real life conversation.

I guess I got a little offended by anyone thinking I would even consider using a tractor to instal SWA cable :)
 
Sorry for misleading you Engineer54 - it's hard to remember every detail when posting a new thread. The to and thro questions and answers don't flow like a real life conversation.

I guess I got a little offended by anyone thinking I would even consider using a tractor to instal SWA cable :)

I've seen tractors and all sorts of other site vehicles/plant used to pull SWA cables into trenches and site ductwork!! It really doesn't work very well at all. Most of that cable needed to be replaced for one reason or the other, usually because of visible stretching and sheath damage. God forbid if i ever saw anything like that being done on any of my projects!! lol!!
 
Only ever pulled cable though 6” welded steel pipe. They went under two railway lines and three roads. Four pipes. 3 X 95mm 11KV PILCSWA and a 185mm 3½ core PVCSWA.
I’ll be honest I wasn’t happy about it. But we did use a torque controlled winch and the correct cable stockings.
The bit I was happy about was welding a stud to the end of each pipe and linking them to the MET.

As for PVC serving pulling back, there’s a simple answer. Cut a couple of foot off the pulled end, cap it and let the cable relax for a week. This job took five years to complete, one week was neither here nor there.
 
Been on a job where we pulled cables in with a scissor lifter before. It was over ground, not through ducts/tunnels however and was helped along with regular cable rollers/shoulders. Worked out fine as we took it at a very steady pace. Really took the work out of moving the weight.
 
Only ever pulled cable though 6” welded steel pipe. They went under two railway lines and three roads. Four pipes. 3 X 95mm 11KV PILCSWA and a 185mm 3½ core PVCSWA.
I’ll be honest I wasn’t happy about it. But we did use a torque controlled winch and the correct cable stockings.
The bit I was happy about was welding a stud to the end of each pipe and linking them to the MET.

As for PVC serving pulling back, there’s a simple answer. Cut a couple of foot off the pulled end, cap it and let the cable relax for a week. This job took five years to complete, one week was neither here nor there.

That's basically the only safe way to pull cables through longish duct runs, the correct cable socking for the cable being pulled, along with ample cable rollers/wheels is an absolute must!!. The torque control on the cable pulling winch is set to data given by the cable manufacturer. The torque control acts like a clutch, which will slip the winch drive out as it approaches the dialed in limit(s).
 
When pulling in cables what would be the best way to attach draw wires to SWA? Only had to do this once threw a 60metre ducting with 25mm 3core and we just drilled a hole threw the cable and threaded the rope threw it…is there any other ways ?
 

Reply to Pulling SWA through a moled hole. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Replies
3
Views
447
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
3K
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
919
So I had a ceiling repair done in my bathroom due to water damage. The neighbors toilet above me was leaking for who knows how long. Mold...
Replies
1
Views
714
When putting in some duct for fibre broadband we also put in a few lengths of 63/50mm twinwall duct "just in case" we needed that, as we knew of a...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock