A relative recently had an electrical certification done on a rented property. The property was build in 2005 and had previously passed 3 electrical certifications with flying colours, however this time round a number of issues arose resulting in a bill of £500, which was very surprising. Several issues, such as RCDs I can trace back to the 2018 changes to the wiring regs, however there was mention of wires terminated incorrectly and needing glanding, which seems strange given that they passed 5 years ago, unless all the previous 3 were wrong. Additionally the cooker was on a 32A circuit breaker, and the engineer said it needed a 40A breaker?? There has been no problems with the 32A breaker tripping, so why was it necessary to increase it to 40A?

I had other issues with plumbing work done by the same outfit following the installation of an electrical shower (it leaked and then leaked after he allegedly fixed the leak). Could you help explain the changes?
 
TL;DR
Want to know if charges for electrical certification are legitimate
What issues were coded C1 and C2 on the EICR, and what were coded C3. C3 is 'improvement recommended" and means just that - recommended but not required.
The wiring regs are not retrospective. If the installation was installed correctly in 2005, any alterations and additions made since then done to the regs at the time they were made and nothing has deteriorated, then it is satisfactory for continued use, but that does not mean that the inspector cannot make strong recommendations for some things to be upgraded.
 
32A on a 10mm is completely fine, no idea why he’s put that down as a C2.

RCD trip time can be up to 300ms, so the 40ms trip time is fine, again not sure why he’s put that down as a C2.

If the SWA hasn’t been glanded the yes this warrants a C2 and will have to be done.

Something that isn’t making sense is that he’s saying there’s a dead short on L-E on your sockets which would mean that your breaker would be going bang every time it’s turned on, which I’m guessing it doesn’t because you would know about this.

This guy either isn’t very experienced with testing or he’s trying to milk money out of you. The only 2 things on there that have to be done are the gland for the SWA and the alleged socket fault, all the others are only C3s and therefore only recommendations. The RCD wouldn’t even be a C3 because it trips well within the maximum time of 300ms so that shouldn’t even be on there
 
OK, from the report there looks to be some valid items, others I would disagree with.

1 - I would really need a photo of the garage board to comment, but even if it isn't glanded properly, providing there is proper connectivity and it achives the level of ingress protection, that would look like an improvement recommend rather than a C2
2 - this aligns with the test report figures, so firstly it looks most likely that a socket outlet has been changed, or whatever and the earth connections haven't been made correctly, this would be a valid unsatisfactory on the report, secondly the low IR reading is difficult to understand, he gives a value of 2.1 somethings! If those somethings are Meg ohm then actually it's technically a pass. If they are k ohms, that's a genuine issue, wouldn't trip the rcd, but is a valid C2, if ohms (which he implies), the rcd would trip all the time.
3 - C3 seems appropriate
4 - what!? C3 at best, if it isn't a problem in practice, then it isn't a problem for the inspection
5 - at 1x 300ms is acceptable, and at 5x 40ms is OK- the rcd appears to meet the standard.


So overall, yes you look to have a valid unsatisfactory with the report, but that's really only the high Zs (sockets at 2.3 ohm) plus potentially the low IR on sockets.

Photos needed to be sure on item 1 but everything else looks like misunderstandings
 
`There is no requirement for a SWA cable to be glanded and earthed at both ends, unless the armour is being used as the earth conductor. If your cable is glanded and earthed at the source end, and is either a 3C cable, with the third core used as the earth conductor, or the garage uses a TT earthing system, then it is fine.
If the garage does use TT earthing, then there must NOT be an (exposed) gland at that end.
 
He has failed to mention the very high r2 for the ring final.
It should also be noted BS7671 does not give minimum values of insulation resistance values for an EICR so 2.1 Meg ohm may not even warrant a mention.
 

Reply to Query on recent Electrical Certification for property in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
761
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
920
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock