Discuss Query on recent Electrical Certification for property in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

He has failed to mention the very high r2 for the ring final.
It should also be noted BS7671 does not give minimum values of insulation resistance values for an EICR so 2.1 Meg ohm may not even warrant a mention.
He does it's squirreled away in item 2 - Zs is to (sic) high
 
5 - at 1x 300ms is acceptable, and at 5x 40ms is OK- the rcd appears to meet the standard.
Where is that time stated on the report?

EDIT: It's okay I see it now.

This is the relevant part of the wiring regs isn't it?
https://electrical.------.org/wirin...nges-to-rcd-testing-in-bs-76712018plusa22022/

Huh, link won't post.

1685215693156.png

So the test results show 54ms at 1x and 23ms at 5x, which as you say are both well within the 300ms (1x) and 40ms (5x) in BS7671.

Thanks
 
Last edited:
Yes, exactly as you found.

Although actually since amendment 2 there is actually no requirement to do these tests as we used to, but it passes in any case
The test was done 10/08/2021 according to the report, so pre-Amendment 2 (28/03/2022). Although the date doesn't really make sense either because the invoice for the work wasn't charged to the owner until Feb 2022, unless maybe the work was postponed due to lockdown following the initial test?? The reason we're looking at it now is because it's very much only the tip of a larger iceberg.
 
Where is that time stated on the report?

EDIT: It's okay I see it now.

This is the relevant part of the wiring regs isn't it?

Huh, link won't post.

View attachment 108444

So the test results show 54ms at 1x and 23ms at 5x, which as you say are both well within the 300ms (1x) and 40ms (5x) in BS7671.

Thanks
Since amendment 2 we only have to carry out the RCD test on 1/2x and 1x. 5x is no longer a requirement
The test was done 10/08/2021 according to the report, so pre-Amendment 2 (28/03/2022). Although the date doesn't really make sense either because the invoice for the work wasn't charged to the owner until Feb 2022, unless maybe the work was postponed due to lockdown following the initial test?? The reason we're looking at it now is because it's very much only the tip of a larger iceberg.
I would question the things that have been mentioned to be only a C3.

The thing that’s probably going to cost you the most is the the fault finding
 
A relative recently had an electrical certification done on a rented property. The property was build in 2005 and had previously passed 3 electrical certifications with flying colours, however this time round a number of issues arose resulting in a bill of ÂŁ500, which was very surprising. Several issues, such as RCDs I can trace back to the 2018 changes to the wiring regs, however there was mention of wires terminated incorrectly and needing glanding, which seems strange given that they passed 5 years ago, unless all the previous 3 were wrong. Additionally the cooker was on a 32A circuit breaker, and the engineer said it needed a 40A breaker?? There has been no problems with the 32A breaker tripping, so why was it necessary to increase it to 40A?

I had other issues with plumbing work done by the same outfit following the installation of an electrical shower (it leaked and then leaked after he allegedly fixed the leak). Could you help explain the changes?
need to pass this report onto the property owner he/ she is the one res[onsibl
 
Bit picky I’d suppose but thinking this is wrong too.
Personally the details here would only be the Main Switch, I would put the RCD on the schedule results page.
I take it’s a Split DB configuration IMG_3938.jpeg
 
Since amendment 2 we only have to carry out the RCD test on 1/2x and 1x. 5x is no longer a requirement

I would question the things that have been mentioned to be only a C3.

The thing that’s probably going to cost you the most is the the fault finding
The work has already been done. The guy has been doing all fixes, electrics and plumbing on the property, which is managed through an estate agent. Basically, they chose the contractors. Since Feb 2022 the charges for repairs amounted to ÂŁ1400(!) on an 18 year-old property, not including EPC and gas certificate. The owner is changing estate agent as a result, but the estate agent defends the contractor to the end and is convinced there isn't a problem and is charging a large fee for the transferral of management. The owner's position, and mine, is that the estate agent has 'substantially failed in their duties' by not finding out last year (when it was first queried) what I found out in a single day, and also not seeing the general problem with the quantity of repair bills on a relatively new property as well as the faulty shower work.

Our main concern now is whether the work he's done is up to scratch, or is that faulty too?
 
2 - this aligns with the test report figures, so firstly it looks most likely that a socket outlet has been changed, or whatever and the earth connections haven't been made correctly, this would be a valid unsatisfactory on the report, secondly the low IR reading is difficult to understand, he gives a value of 2.1 somethings! If those somethings are Meg ohm then actually it's technically a pass. If they are k ohms, that's a genuine issue, wouldn't trip the rcd, but is a valid C2, if ohms (which he implies), the rcd would trip all the time.
Okay thanks.
 
Last edited:

Reply to Query on recent Electrical Certification for property in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
761
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
921
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top