telectrix

-
Mentor
Esteemed
Arms
Reaction score
67,273
now this is not exact, but comes close. say you have a 3 phase, 400v motor, given the kW, to get an approx. value for the current per phase, (can be done in your head), just multiply the kW x 1.5. e.g. a 20kW motor. I = 30A. ( not allowing for efficiency, pf etc. ) just to give a rough idea.
 
might be better if you double it as i do it more accurate but still a rough figure.
18.5 Kw motor = 35amps
22 Kw motor = 40amps ...... this trend to be a few amps off either side works up to 22kw then the values start to be several amps out after that.

30Kw = 54amps
37Kw = 65.5amps

Note im refering to motors with a plated voltage of 415v that are usually the majority of existing motors in use, you are using 400v plated value hence the difference but if you know both these rough guides its a good start.
 
i get 53.4A for a 37kW.

37,000/(1.732 x 400)
 
Ive just done a 30kw and a 22kw motor existing on a machine and the plated ampage does match my examples give or take a few a few amps, i can only assume modern motors have a better efficiency than the older ones, its a rule of thumb that can catch you out if you are looking at older machinery and yes Tony i probably am as its a guide ive always used and found to be accurate, as it omits the need to allow for PF and efficiency issues.
 
appreciate that pf and efficiency will increase the current required. my post was just to get a starting point. obviously when designing a circuit to power any machine, all factors must be taken into consideration, otherwise you either get an under rated circuit, or spend more on cable than necessary.
 
I normally work on 4.5A/kW when pricing up and it normally is reasonably close. However, i always go "next size up" so i don't come unstuck on the price.

20kw x 4.5 = 90A / 3phases = 30A/phase

Always worked for me :)
 
which gives the same answer as my guesstimate. 20 x 1.5 = 30A.
 

Reply to quick rule of thumb, 3 phase current in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
0
Views
249
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hello all, I recently was asked to quote a three phase motor install within a pallet factory. To be honest, I was somewhat stumped in how to...
Replies
3
Views
2K
Hello everyone, I really hope this isn't an idiot question but boy, I'm out of my depth! I've spent about 3 weeks (not solid mind) trying to work...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock