Discuss R, L, C and Power Question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

jaydub

-
Reaction score
24
Question: Three coils of resistance 40 Ω and inductive reactance 30 Ω are connected in delta to a 400 V 50 Hz three phase supply. The total power will be:

a) 13.31 kW

b) 7.68 kW

c) 9.6 kW

d) 16.63 kW

I now know what the answer is, however, I do not understand how to get there! I would be very interested to see what others think to this.

I will hold back the correct answer for the time being.
 
Now that is what I believe to be the answer. I also managed to get there using two different formulas.

However, according to the answers, that is not correct! Guess again :D
 
The answer is apparently B, 7.68kW.

Would anybody be able to explain how to carry out the calculation? I have looked at the PDF Vortigern, but I still don't understand it... :rolleyes:
 
I thought you had to do this:

Z = square root of (Rsquared + XLsquared)

Z = 50 ohms

400/50 = 8amps

400 x 8 = 3200W

3200 x 3 = 9600W OR 9.6kW

Clearly though, this is incorrect, static zap, can you shed any light?
 
I found this part of the course I did the most exacting and understood it at the time, however I cannot get my head around it now without serious study and thinking about it. It is a different thing with the tutor there helping you to get through it and as I virtually never used it in general work it just goes away. This is for the industrial electricians I think. I am sure there must be some on here.
 
the last time i did any calculations like this, calculators had not been invented. a computer was the size of a house, and we still had steam trains. so i sit this one out.
 
Can you possibly show the working out to get the answer below please?
Read thru post( 7) ... the last good line reads =8Amps
(ignore everthything from then on)

The final answer is 3x the answer for 1 phase , so divide B= 7.68 /3 for clues !
Post (10) has the other formula needed .
" Copper Losses " is probably a good google phrase

(compared with other examples , impedance bits are handed on a plate )
(No Pi , frequency, current etc to get confused/distracted by hunger with )
 

Reply to R, L, C and Power Question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
758
I will describe my problem in as much detail so you guys might be able to answer my question. I am never home, my Electric bill is $ 28 to $30 a...
Replies
23
Views
1K
Hi All, I am currently learning about AC and DC supplied coil and have been given the scenario below. I understand the first few steps but then...
Replies
1
Views
1K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock