Discuss R1 R2 - Explanation help in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
I'm just starting up and need to have a question cleared up as I've asked a few other sparks and can't get an answer. So if anyone can help me out I'd appreciate it. When doing an R1 R2 test I've seen a few videos where they connect the live into the earth bar and then carry out the test at the switch. My question is that doesn't the parallel paths of the other CPC's effect the result. Why are both live and CPC not isolated like on the R1 R2 for a ring test.
 
I'm just starting up and need to have a question cleared up as I've asked a few other sparks and can't get an answer. So if anyone can help me out I'd appreciate it. When doing an R1 R2 test I've seen a few videos where they connect the live into the earth bar and then carry out the test at the switch. My question is that doesn't the parallel paths of the other CPC's effect the result. Why are both live and CPC not isolated like on the R1 R2 for a ring test.
may I ask in what capacity have you done any testing .
 
I'm just starting up and need to have a question cleared up as I've asked a few other sparks and can't get an answer. So if anyone can help me out I'd appreciate it. When doing an R1 R2 test I've seen a few videos where they connect the live into the earth bar and then carry out the test at the switch. My question is that doesn't the parallel paths of the other CPC's effect the result. Why are both live and CPC not isolated like on the R1 R2 for a ring test.
All parallel paths should be removed as far as reasonably practicable when testing for initial verification using the R1+R2 continuity of cpc testing method.
The method i use is to remove the cpc from the earth bar and remove the line conductor from its OCPD and temporary join together.
 
There is nothing wrong with linking a fly lead from the earth bar. When you think about it, this will give you a more accurate understanding of what your Zs will be.
 
There is nothing wrong with linking a fly lead from the earth bar. When you think about it, this will give you a more accurate understanding of what your Zs will be.
This does not remove parallel paths such as say a bonding conductor connecting to the gas pipe.
If you are testing say a boiler circuit then if you don’t remove parallel paths then you will most likely get a lower reading back through your bonding conductor which may mask the fact your cpc is discontinuous.
Zs testing is done with all parallel paths connected and the installation energised having confirmed that all cpc’s are continuous but we are talking about R1+R2 testing.
This is referenced in GN3.
 
If its a new install R1 R2 testing would be done before final connection are made at the consumer unit , but durring an eicr it may not be practical to remove the circuit from the consumer unit so it will not be posible to avoid testing a circuit with parellel earth paths, in an ideal world you would have the original eic to cross referance the results , but in the real world you would have more chance off having next weeks lottery results , so you would have to use your experance to determine if the result is satisfactory
 
If its a new install R1 R2 testing would be done before final connection are made at the consumer unit , but durring an eicr it may not be practical to remove the circuit from the consumer unit so it will not be posible to avoid testing a circuit with parellel earth paths, in an ideal world you would have the original eic to cross referance the results , but in the real world you would have more chance off having next weeks lottery results , so you would have to use your experance to determine if the result is satisfactory
I wouldn’t bother to do R1+R2 testing on an eicr.
I’d just measure Zs of the circuit.
Use a R2 wander lead and a visual test to confirm exposed conductive parts are connected to the source of earthing
 
The testing on a ring circuit is different from radial. There are books that show the live cable of the radial in with the cpc of the same circuit in the the earth bar. A ring main continuity R1 and R2 test requires crossing over 4 cables that is way you cant just stick all four in the earth bar. it will spoil the path of the ring. A live Zs test, on radial, might give an closer reading that matches the calculated R1 R2 reading added with the Ze, if it is connected to the earth bar because they both went through parallel earth paths.
 

Reply to R1 R2 - Explanation help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
490
Hello, Hoping to get some advice on R1 + R2 radial testing and best practise. When doing R1 R2 instead of taking cables from mcbs/rcbos and the...
Replies
1
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock