Discuss R1+R2 mixed installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

dcwuk

-
Reaction score
0
Carrying out a few consumer unit replacements at a hotel, installation to the room is via trunking conduit with no cpc however at the rooms previous refurbishments have been carried out these being wired in Twin and earth with the cpc being connected to the existing system. Now I am not sure what to record as the R1+R2 results do I add a limitation or calculate from the Zs Ze readings and state that's what I have done?
 
If there is no CPC then you really need to be dealing with that situation first!

However if what you mean is that the trunking/conduit is the CPC then you just measure the R1+R2.
 
Sorry should have made that clear, the trunking and conduit installation is steel and up to the rooms is the CPC. I was of the opinion that the R1+R2 results would be meaningless to a point because of all the parallel earths? Thanks for your reply BTW
 
Carrying out a few consumer unit replacements at a hotel, installation to the room is via trunking conduit with no cpc however at the rooms previous refurbishments have been carried out these being wired in Twin and earth with the cpc being connected to the existing system. Now I am not sure what to record as the R1+R2 results do I add a limitation or calculate from the Zs Ze readings and state that's what I have done?

One thing you never do is calculate a R1 + R2 this always needs to be measured. Get your meter out ant test either R1 + R2 or else R2. I would be concerned as how the cpc's in the twin and earth are connected to the containment system.
 
One thing you never do is calculate a R1 + R2 this always needs to be measured. Get your meter out ant test either R1 + R2 or else R2. I would be concerned as how the cpc's in the twin and earth are connected to the containment system.

Thanks for your reply. within the room there is a steel skirting trunking the socket outlets being earthed via a fly lead lugged and bolted through the trunking. The bedhead lighting is fed via flex outlet plates fixed to the trunking and flexes up behind the bedhead to the light fittings. The bathroom has a some point been refurbished and is wired in T&E to an adaptable box behind a bulkhead above the bathroom sink. the adaptable box is inaccessible but I can see that the CPC is lugged an bolted to the box not ideal I know but the Hotel is not about to let me remove all these bulkheads to access the box. The distribution is in a central location in the corridor the furthest room being approx. 25m from this location. Because the Hotel is occupied I am trying to minimize the amount of time the rooms are out of service and to test in the quickest and most accurate way. I will likely do as you suggested and carry out an R2 test and add a limitation to the test certificate for the R1 and R2 readings. There in total 26 distribution boards to replace throughout the hotel these being Simplex and fitted with 30a and 5A type 4 3871 mcb`s. This is part of the remedial works that comes from a fixed wiring inspection by the insurance company and mainly involves installing RCD protection to the room/bathroom circuits. At the moment I am carrying out this work on my own and as I wrote above trying to minimize the inconvenience to the Hotel.
 
You shouldn't need to remove all the bulkheads. Sample them there could be MF joints in there. If that's why you wouldn't to remove them?...

An R1+R2 doesn't have to be made up of cable only, it could be containment if that's whats been used. Do your R1+R2 or R2 as you usually would. Using a wonder lead your still measuring the same earth path just minus line conductor of course. There's no need for any limitation you either use method one or two and N/A in the box not used.
 
P.S 26 distribution boards to replace?! Is that necessary?...
I`m not looking too hard :) The report says the type 4 mcb`s are obsolete and I believe they need a current in the region of 50xIn to operate but its mainly because of the lack of RCD protection to the rooms and public areas and you cannot get RCBO`s or pods to fit these. The original installation was conduit and trunking throughout and is still sound but there have over time been so many upgrades to the installation and these have been carried out in T&E for the most part so RCD protection comes into play within the fabric of the building as well. Thanks for the reply which confirms my intended method of testing this job.
 

Reply to R1+R2 mixed installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
612
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
455
Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock