Discuss R1 R2 test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

nicsin02

When doing a periodic test we have been advised by SELECT that we only have to measure or Zs and calculate our R1 R2, issues have been raised such as what if the circuit doesn't have it's own c.p.c and is merely passing on the basis of picking up a parallel path somewhere, obviously this would fail the R1 R2 test, what is your thoughts guys, cheers
 
Like all testing I think has the tester you have to test as you see fit, that should include many factors, current condition of the installation, type of installation, environment etc.

In a domestic situation I could not see a situation where you would never carry out an R1 +R2 test.

Commercial/Industrial can be different. There is call for an R2 test especially on things like Hi-bay lighting, Circuits where you literally can not isolate for any period and so on.
 
Would never think of calculating R1+R2 if not done state its not tested on the EICR along with the reason.
 
It must be a different GN3 to the one I have.

I think it is roughly translated as Test method 2 can be used to confirm continuity of protective conductors etc.

I might be wrong with my thinking!
 
It must be a different GN3 to the one I have.

I think it is roughly translated as Test method 2 can be used to confirm continuity of protective conductors etc.

I might be wrong with my thinking!

no your dead right, gn3 states that test method 2 may be used to confirm continuity. But whichever method is used, continuity must be confirmed
 
Years ago was doing a test on a lighting circuit where the conduit system was the Earth, Zs reading was fine, but was open circuit doing the R2 test! Turned out that the conduit had rusted away and testing at 230/240V it would test fine through the rust and damp, but the low ohms test at 12v came up as open circuit.

Im sure I read somewhere that you have to test R2 and can then calculate the Zs from that but not the other way round.
(dont have books to look it up at the moment thought)
 

Reply to R1 R2 test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
881
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
674
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Have only recently gotten in to testing. Doing an R1+R2 on a lighting circuit but instead of producing a result my tester clicks over and over...
Replies
5
Views
947
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock