Hi guys,

Just an initial heads up, I’m just level 2 qualified, so go easy on me.

I’m currently adding some sockets in my house. So I thought I’d break the ring, extend it and add them in.
Took the back off a socket and it only had one cable going into it, so presumed it was a radial. I’ve gone back to the board and there’s only 2 32A MCB’s. One ring up stairs and 1 down. So presumably these 2 sockets are a poor designed spur off the downstairs ring, not meeting regs.

It’s obviously not well rated incase it exceeds the 26A of the cable having 2 double sockets, so I need to make it safer somehow.

My initial thinking was to put in a fused spur to protect the cable, but one of the sockets is used with a kettle, so a bit more load and it’ll overload the 13A fuse.

So, could I make it so there’s like a garage board hidden away with a 20A MCB at the beginning of the spur and make it into a sort of radial off of the ring?

Cheers in advance for replies
 
Hi guys,

Just an initial heads up, I’m just level 2 qualified, so go easy on me.

I’m currently adding some sockets in my house. So I thought I’d break the ring, extend it and add them in.
Took the back off a socket and it only had one cable going into it, so presumed it was a radial. I’ve gone back to the board and there’s only 2 32A MCB’s. One ring up stairs and 1 down. So presumably these 2 sockets are a poor designed spur off the downstairs ring, not meeting regs.

It’s obviously not well rated incase it exceeds the 26A of the cable having 2 double sockets, so I need to make it safer somehow.

My initial thinking was to put in a fused spur to protect the cable, but one of the sockets is used with a kettle, so a bit more load and it’ll overload the 13A fuse.

So, could I make it so there’s like a garage board hidden away with a 20A MCB at the beginning of the spur and make it into a sort of radial off of the ring?

Cheers in advance for replies
The socket you described as against the Regs, could be a single spur from 1 of the RFCs nothing wrong with that.
Your copy of BS7671 Appendix 15 will describe standard circuitry for socket outlets take a look and think again.
 
Hi guys,

Just an initial heads up, I’m just level 2 qualified, so go easy on me.

I’m currently adding some sockets in my house. So I thought I’d break the ring, extend it and add them in.
Took the back off a socket and it only had one cable going into it, so presumed it was a radial. I’ve gone back to the board and there’s only 2 32A MCB’s. One ring up stairs and 1 down. So presumably these 2 sockets are a poor designed spur off the downstairs ring, not meeting regs.

It’s obviously not well rated incase it exceeds the 26A of the cable having 2 double sockets, so I need to make it safer somehow.

My initial thinking was to put in a fused spur to protect the cable, but one of the sockets is used with a kettle, so a bit more load and it’ll overload the 13A fuse.

So, could I make it so there’s like a garage board hidden away with a 20A MCB at the beginning of the spur and make it into a sort of radial off of the ring?

Cheers in advance for replies

I think you may be describing 1 double socket as 2 outlets, if so there's no need to worry as you can have one single or double socket spurred from any part of the ring circuit. Of course if you wanted to run additional sockets from this point you'd have to fit a 13a fused spur before the first existing socket. But in certain circumstances I've been known to use a 16a MCB in a small 2 module enclosure. :)
 
I agree with daveOCD in part mate I think your describing 1 double socket as 2 sockets but its OK to spur yo a double the reason I think that is in your description you only mention opening 1 socket up assuming you fint have a test kit which most trainees don't let's face it. what I would do is open up all the sockets local yo it including above on the other floor. Find the one with three cables in. Isolate the system. Separate the cable ends re energise the circuit inform people first then go and see how many double sockets are dead if its just 1 then don't worry but if its two dead then you will need to sort it like Murdoch said. Hope that helps mate I'd I were you I'd get telectric to come have a look offer him a days labour on return ypu will learn
 
Took the back off a socket and it only had one cable going into it, so presumed it was a radial.


So presumably these 2 sockets are a poor designed spur off the downstairs ring

It’s obviously not well rated incase it exceeds the 26A of the cable having 2 double sockets


one of the sockets is used with a kettle


:confused::confused::confused:




Breaking the post down and noting the important words for each sentence we have :)

A socket
One cable
2 sockets
2 double sockets
One of "THE" sockets

OK that seems to have cleared it up for me ;)
At least I think its clear :eek:
 
Arguing over small details when I’d rather have a solution. To clear it up...hopefully. I have a spur off of the ring coming from a junction box. This spur has 2 double sockets on it (non-compliant)
 
Thanks for clarifying. Important to have all the information.
 
Arguing over small details when I’d rather have a solution. To clear it up...hopefully. I have a spur off of the ring coming from a junction box. This spur has 2 double sockets on it (non-compliant)
so you have the choice of 2 options:

1. recable to the spurred sockets with 2.5mm and to any new sockets reinstate rthe ring.

2. fit a FCU at the start of the spur.
 

Reply to Radial or spur off of ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
268
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
660
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
727
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock