Discuss Random socket tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi,

Our breaker box is located in the cellar. We experience random socket trips throughout the year. Summertime seems to be the best when we can go months without an issue.

Autumn/winter time is awful. We have had 3 trips within the last 24 hours. No new appliance has been switched on when the trips occur.

Could it be a faulty RCD? Is it the location of the breaker box? Please help.
 
Is there any signs of condensation on the consumer unit or in the cellar?
 
If you have a dehumidifier you could try putting that near the consumer unit and see if that helps.
 
Hi Fuz and welcome to the Forum:) .
Repeating trips don't happen for no reason and aside from the inconvenience to you it could be a fault that's getting worse and so may become dangerous at some point. If it's not related to an appliance then as Buzz has advised, I think you'll be best served by getting your local friendly Electrician around to have a look. Most do "attend and work for an hour" callouts. Someone here may be nearby (?).
 
The lights are on a different rcd and the only outside socket has a built in rcd which is tripped when not on use. May have to bite the bullet and get the sparky in

That socket is most probably the problem.
Moisture inside will still trip the circuit RCD even though the socket RCD is off.
 
Fuz, what actually trips, is it the RCD for a set of mcb’s, or is it an individual mcb that keeps tripping?

If it’s the mcb, is there a label below it that says what circuit it’s protecting and what is plugged in to the sockets of this circuit?
 
Yes it's the rcd that protects just the sockets. Everything else stays on.

haha.. wish you would have put this in your original post mate.
Does look like the outside socket is causing all the trips then... but can't be 100% sure, unless you get someone to look at it.
 
haha.. wish you would have put this in your original post mate.
Does look like the outside socket is causing all the trips then... but can't be 100% sure, unless you get someone to look at it.
The outside socket has a built in rcd. When it is not in use we trip it on the outside socket itself.
 
The outside socket has a built in rcd. When it is not in use we trip it on the outside socket itself.
But if water is getting into the outside socket it will still trip the RCD in your board.

The socket RCD will only protect what is plugged into it.
 

Reply to Random socket tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Calling all electrical professionals / boiler tradesmen -WE NEED YOUR HELP! Every so often (twice in the last two days) when running the hot...
Replies
15
Views
447
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
480
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
566
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock