sevuk

-
Reaction score
33
Rcbos haven't caused me much concern before but I'm wiring a board of 44 and it's triggered my paranoia. I've also sent the below to schneider.

I normally just disconnect the line and neutral for testing between live conductors and then test lives to earth with the earth tail of the rcbo and earth conductor still connected to the earth bar at 500v

My question is this correct? Could the test still be carried out in an isolated board with the neutral still terminated in the rcbo but the line disconnected. (Basically to clip onto the neutral bar and test individually to each disconnected line.)

Also the reverse could insulation testing be done with the neutral disconnected from each rcbo to test the insulation between phases?

From a technical point of view are we just trying to avoid putting the meter between line and neutral while both are connected as it's the potential between these that could damage the unit? And does it matter in any circumstance that the earth is connected?
 
If you IR test a RCD or a rcbo you will get very low results...

So best avoid multiple IR tests together.

Quite sensible really. I talked to schneider, they want you to disconnect every rcbo entirelt to do insulation resistance tests. With a fully populated board you'd have to disconnect all of them to do an IR. This is madness right?

If you were to disconnect line and neutral why would it be adverse to then ir test live to earth it's still connected to the rcbo? There's no voltage across the core with the lives disconnected.
 
With a fully populated board you'd have to disconnect all of them to do an IR. This is madness right?

Well, as a fan of RCBO's I don't see this as a problem ......... and if you are testing due to the RCBO testing, you need to do this on the circuit affected ..................... to get accurate results...
 
Thinking about it you're right. It normally wouldn't be a big deal but there are 44, though still not the main issue. It's a board with all the earth terminals at the top and the guy before me glanded all the armoureds to the top instead of mounting a trunking on first making the earths a pain to disconnect and reconnect.

What I mean is if the live conductors are disconnected, there's no path to earth so I can't see why you'd get a reading to earth unless there was a fault or insulation degradation. You would get readings if you tested to the neutral bar though.

Anyway in the installation phase there would be ways to ir test the circuits first before connecting them to the rcbo, but during service if you had to disconnect even the earth doing any ir tests require full isolation of the board which wouldn't be practical.
 

Reply to Rcbo paranoia in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
673
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
760
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
732
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
973
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock