Hello Guys,

Can you help with a problem we had today.

We have installed a ring circuit of exterior 70 watt MHi floodlights around the perimeter wall of a building. There are 16 lights on a ring of fire tough 2.5 R1 + RN with 1.5 R2.
The cable length is 230 meters. The ZS = 0.71. R1 = 1.59. RN = 1.59. R2 = 0.95.
We installed a 16 amp 10K RCBO but the reading we got on RCD test were X1 550/550 X5 440/ 440.
Both reading outside of Bs7671.
These reading were obtained with a raw circuit, straight out of the RCBO into the ring.
Does anyone have an idea why the readings were so high so as not to comply?
We have as a temporary measure (we hope) installed a MCB with no problems.
Regards
Gadget.
 
Were the lights connected whilst you were testing as they may have been "balancing" the differing load and delaying tripping.
An RCD test should ideally be done with no loads on the RCD and tested at the RCD terminals.
Try testing the RCBO without any circuit attached.
 
could be with frire tuff. the foil is in contact with the cpc thus increasing the effective csa.
 
The figures quoted are what we got.

Strange yes but the only way for us to go from here is to.
1) Disconnect all the light fittings and retake measurements.
2) Also carry out test on foil of fire tough to see if any contact with CPC
to alter the prospective results.
Many thanks guys.
 
The figures quoted are what we got.

Strange yes but the only way for us to go from here is to.
1) Disconnect all the light fittings and retake measurements.
2) Also carry out test on foil of fire tough to see if any contact with CPC
to alter the prospective results.
Many thanks guys.

You will not need to disconnect all the fittings simply switch off, or remove the cables from, the MCBs in the board (when it is off!) so that no load is connected to the RCD once you start testing.

The foil of the cable should be in contact with the CPC as this is the design of the cable; the effect of this is to have a large cross sectional area cpc which will have a lower resistance than the line and neutral conductors (i.e. for your ened to end values 0.95 is less than 1.59)
 
The foil of the cable should be in contact with the CPC as this is the design of the cable; the effect of this is to have a large cross sectional area cpc which will have a lower resistance than the line and neutral conductors (i.e. for your ened to end values 0.95 is less than 1.59)

I've not used this type of cable before so it's nice to learn this. Thank you :thumbsup
 

Reply to RCBO test Results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
730
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock