Been testing today on a new installation, it was a lighting circuit all lighting weird via click roses. Came to the rcbo test, trips on 5x at 100ms then says plus 40 on 5x. Quickly swapped out rcbo thinking it was just faulty and does same again with the new one. Some rooting around in loft i notice the air con lads have connected a air handling unit to the circuit, not a prob as they dont take many amps, disconnect it and retest, 28ms on 5x, anyone else had this happen before? something to do with the motor perhaps? ask the aircon lads and they say never had it before, they checked the unit and all was working fine with the unit, just baffled me abit thats all.
 
If there is a capacitance effect on the circuit, as can come from connected equipment, particularly electronics, then this can prevent the current being introduced on to the circuit by the tester from being registered as it is being briefly stored.
It is generally best to test an RCD with no connected load on the circuit.
 
You would notice very similar results when RCD testing and a fridge still plugged in as well , as said always best with all loads disconnected ....
 

Reply to rcbo trip question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
751
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
404
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
875
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock