Hi all,


I'm having a problem with a newly installed RCBO. Having made alterations to a lighting circuit in a bathroom I recommended to the builder that the MCB on a 16th edition consumer unit on the non-rcd side be replaced with an RCBO as per 17th edition. I completed continuity ok, insulation resistance 0.54, not great! Attempted to turn on RCBO and it won’t turn on. Fault on the wiring. I hate fault finding. Why won't it just work. I put the MCB back no problems. Tomorrow I have to do the usual thing and explain to the customer why I emptied there linen cupboard to install an RCBO which they haven’t asked for and that I have no idea how long it will take to resolve the issue. What concerns me is that if It were a borrowed neutral this would allow the rcbo to be turned on but trip when under load? The rcbo not turning on is disconcerning.
 
Faulty RCBO? can happen.

If everything is checking out with tests, then its a possibility.
What was the alteration? can you isolate parts of the circuit to pinpoint what might be the cause?

I had a problem last week where a new kitchen under cabinet LED would trip the main RCD every 3rd or 4th switch operation. Replaced the driver and all is well.
 
Hi all,


I'm having a problem with a newly installed RCBO. Having made alterations to a lighting circuit in a bathroom I recommended to the builder that the MCB on a 16th edition consumer unit on the non-rcd side be replaced with an RCBO as per 17th edition. I completed continuity ok, insulation resistance 0.54, not great! Attempted to turn on RCBO and it won’t turn on. Fault on the wiring. I hate fault finding. Why won't it just work. I put the MCB back no problems. Tomorrow I have to do the usual thing and explain to the customer why I emptied there linen cupboard to install an RCBO which they haven’t asked for and that I have no idea how long it will take to resolve the issue. What concerns me is that if It were a borrowed neutral this would allow the rcbo to be turned on but trip when under load? The rcbo not turning on is disconcerning.
0.54 what and between what?
 
No point whingeing about why don’t you grab your test kit and start fault finding. If you designed the install you need to live with your decision and fix the problem.

I designed the small alteration ie: made a pull cord into a light switch. Then went to the board only to find no rcd protection for a low voltage circuit in a location with a bath/shower.
 
bet i could turn it on:

2b31cc7ab346d8e84b477b9f0cbf115e--sexy-women-sexy-girls.jpg
 
Hi all,


I'm having a problem with a newly installed RCBO. Having made alterations to a lighting circuit in a bathroom I recommended to the builder that the MCB on a 16th edition consumer unit on the non-rcd side be replaced with an RCBO as per 17th edition. I completed continuity ok, insulation resistance 0.54, not great! Attempted to turn on RCBO and it won’t turn on. Fault on the wiring. I hate fault finding. Why won't it just work. I put the MCB back no problems. Tomorrow I have to do the usual thing and explain to the customer why I emptied there linen cupboard to install an RCBO which they haven’t asked for and that I have no idea how long it will take to resolve the issue. What concerns me is that if It were a borrowed neutral this would allow the rcbo to be turned on but trip when under load? The rcbo not turning on is disconcerning.
why wont it just work? because someone has wired it up incorrectly

the whole point of testing is to find out faults BEFORE turning the magic back on

id rather fault find than carry hundreds of storage heater bricks to the top floor of a 5 floor building
 

Reply to RCBO will not turn on in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
Last week I took the opportunity of having the mains power off to test the RCBOs in a Wylex Consumer Unit, fitted nearly 5 years ago, which has...
Replies
2
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock