Discuss Rcbo??? in the Australia area at ElectriciansForums.net

K

Kev2632

fr_57_size880.jpg

Im scratching my head here at this, its probably because of the time off night but i cant get my head round this at all, here in the picture is a contactor for the outside lights, now this is one of many contactors throughout the building. there is contactors at each consumer but there is 1 Photocell controlling everything,so all the contactors was linked out to bring them in at the same time. Now every circuit is on its own RCBO, you will notice that they have joined all the neutrals in a connectore block, wouldnt that affect the RCBOS? as they are all coming from different circuits??
 
Yea but what im meaning is you will see how they have all the neutrals joined together for the supplys and the control side of the contactor, but they are off different Circuits, so wont the RCBO trip as all the neutrals are connected together?
 
all of the neutrals would be connected together on the neutral bar anyway

So it doesnt matter if other neutrals are joined together with each other then?? where as if it was say like a split load RCD board and the neutrals were all joined together it would trip wouldnt it?
 
Not when RCBOs are used they aren't.


Im just trying to get my head round it grr its late haha, but i keep comparing the RCBO'S to like a split load RCD Board, why is it that you can connect all the neutrals together like that on RCBO's but if i was do something like that with a split RCD board it would trip the RCD because it sharing neutrals from a different RCD's??
 
I think the problem here is that because it is controlled from a photocell everything switches on at the same time, so it is possible that the RCBO isnt sensing a imbalance in the conductors. The only time it would trip a RCBO is if there is something switched on and the other RCBO is receiving the neutral imbalance.
 
Looking at the Picture there only appears to be 2 wires going into the Contactor what you may have is a single RCBO supplying the contactor and multiple circuits going from the contactor to the lights hence the reason why all the neutrals are joined ,looking at the picture it looks like a 3 phase board with the tripple pole being marked L1L2L3 , looking at the contactor again it looks like just one of the contacts is being used , it may be me as i shouldnt have gone to specsavers , what can be done is a Day light sensor having a low current capacity using a Contactor with a higher current rating , or am i totally looking at the worng pic
 
The final circuit neutrals will have to be separated.

That's why they are connected to the top of the RCBOs and not to a neutral bar.
 
I think the problem here is that because it is controlled from a photocell everything switches on at the same time, so it is possible that the RCBO isnt sensing a imbalance in the conductors. The only time it would trip a RCBO is if there is something switched on and the other RCBO is receiving the neutral imbalance.

im having a stupid moment here to myself, sorry im not explaining myself properly

there is no fault with this photo,

All im trying too get my head round is, Why on RCBO can all the neutrals by connected together on the 1 neutral bar? wont the other RCBO see any imbalance from the other ones? because i know on a 240v Split load RCD board you cant share neutrals from other RCD'S so why can you connect all the neutrals together on RCBO'S?
 
Being old and a little short of eagle eyed,I have difficulty seeing the detail in the picture
i will make a comment though

Are you sure its circuit neutrals that you believe you are seeing connector blocked ?
Its probable the contactors are switching the lives only and what you are seeing is the coil feed and neutrals in and then out to the next contactor, all these fed from one circuit down the line
 
Being old and a little short of eagle eyed,I have difficulty seeing the detail in the picture
i will make a comment though

Are you sure its circuit neutrals that you believe you are seeing connector blocked ?
Its probable the contactors are switching the lives only and what you are seeing is the coil feed and neutrals in and then out to the next contactor, all these fed from one circuit down the line
im having a stupid moment here to myself, sorry im not explaining myself properly

there is no fault with this photo,

All im trying too get my head round is, Why on RCBO can all the neutrals by connected together on the 1 neutral bar with there neutral lead? wont the other RCBO see any imbalance from the other ones? because i know on a 240v Split load RCD board you cant share neutrals from other RCD'S so why can you connect all the neutrals together on RCBO'S?
 
Last edited by a moderator:
The rcbos are likely to be single pole,the outgoing neutral will be the circuit load side
The feed neutrals of the rcbos are looped at the neutral bar
Where are you thinking that the neutrals are being grouped?

The neutrals have to go through the rcbo to maintain balance
If there are any parrallel paths for that neutral,it will imbalance
 
Last edited:
I see that makes sence now ,your flying lead of the neutral is the neutral the circuit neutral is connected to the electronics of the RCBO so balancing out the RCBO exactly as the Live is so realy its live and neutral in through the electronics then out if that make sence
Z
 
Last edited by a moderator:
I see that makes sence now ,your flying lead of the neutral is the neutral the circuit neutral is connected to the electronics of the RCBO so balancing out the RCBO exactly as the Live is so realy its live and neutral in through the electronics then out if that make sence
Z

yea i understand what you mean,so in theory in relation to that photo then, there is no chance of the final circuits (NEUTRALS) being joined together in that connector block then? as there is two different RCBOs supplys there
that would trip it yea?
 
Correct as before they hit the load side where its balanced it goes through the electronics ,its like a wall between the supply neutral and the load neutral if you connect 2 load neutrals together it will trip just like in dual RCD boards when you have a shared neutral
 
so basically your saying the Neutral LEAD is the supply neutral to each circuit then yea? it goes out on the live round the circuit and back through the neutral, through the electronics, and up the neutral lead yea? is that right?
 

Reply to Rcbo??? in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
940
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
756
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock