I use a Dilog 9083P MFT, which was recently calibrated.

Have just finished extending a ring circuit at a customers house. All testing OK until i used the 'auto test' function to test the 30mA RCD at 5 x IʌN @ 0º, the trip time showed >40mS. All other tests were within limits (5 x IʌN @ 180º was 19mS)

When I manually selected the individual 5 x IʌN @ 0º setting, the trip time was 23mS.

Tried it again on the auto setting and a reading of >40mS was displayed.

Is there something in an auto test function that could cause this?

I'm aware that there can be an anomaly when performing direct Zs readings on some testers with a 'no trip' function, but are there any similar anomalies on the auto test RCD function?

Many thanks
 
if you've used the tester plugged into a socket, the results can be affected by the circuit itself. try testing at the RCD with no circuit connected if you get strange readings otherwise.
 
if you've used the tester plugged into a socket, the results can be affected by the circuit itself. try testing at the RCD with no circuit connected if you get strange readings otherwise.

Thank you

Heading back tomorrow to finish a couple of other items. I had just used the plug in adapter in a socket. Will re-test at the RCD and see what happens.
 
bit of a pain having to switch RCD back on and keep the probes in contact. another possibility is the MFT warming up during auto test. funny things these modern gadgets can be. i still rely on a 40 year old analogue megger for fault finding.
 
Depending on the test equipment, components can sometimes store electrical charge which needs to be discharged when REPEATEDLY testing. Turn the mechanical dial fully clockwise and anti clockwise a few times to discharge components before retesting.
 
Depending on the test equipment, components can sometimes store electrical charge which needs to be discharged when REPEATEDLY testing. Turn the mechanical dial fully clockwise and anti clockwise a few times to discharge components before retesting.

Thank you. I'll give it a try. Unfortunately didn't get a chance to test it at home as a comparison.
 
Thank you

Heading back tomorrow to finish a couple of other items. I had just used the plug in adapter in a socket. Will re-test at the RCD and see what happens.

I have never seen the sense in plugging a tester into a socket to test an RCD.

It's the RCD that you're testing so test the RCD at the RCD without other complications getting in the way, then you KNOW you've tested the RCD!
 

Reply to RCD auto test function in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
804
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
710
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi folks. Im a RECI contractor based in Co Sligo, Ireland . I was doing erroneous testing on a domestic board which gave me readings between 90V-...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock