When does an installation NEED an RCD? I thought that all new circuits need one but I now believe that I am mistaken.

Regulation 411.3.3 for socket outlets up to 32amps and regulation 411.3.4 for lights.
Then for special locations like bathrooms.
If the cables are less than 50mm deep into the wall

So when I'm installing a new oven, boiler or any fixed equipment really I don't technically need an RCD protecting the circuit? Unless ofcourse the manafacturer's instruction say so.

thanks
 
As you have said RCDs are required for specific things only, there is no blanket requirement for RCDs on all circuits.

In practice the vast majority of new final circuits in a domestic installation will need RCD protection due to cables being buried at less than 50mm etc, serving a bathroom, serving lighting circuits or being the easiest way to RCD protect the sockets.
 
If doing a like for like swap then you wouldn't technically need to install an RCD however it would always be advisable to recommend to the customer that one is installed if required.
 
How many boilers have thier own feed? I suspect most are just taken from a FCU off the nearby ring and get whatever it has! (Which these days ought to be RCD protected)
 

Reply to RCD for boiler replacement? When is an RCD NEEDED? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Had a new unvented Boiler fitted as the old one had reached the end of it's life. Electrician mentioned that it might be worth replacing my fuse...
Replies
11
Views
1K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
580
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock