Discuss RCD Plugs in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

G

Graeme Moo

Can anyone tell me a PRACTICAL reason for installing RCD plugs to class 2 site equipment, and how do i PAT test the actual appliance without removing the RCD plug?
 
When you say site equipment, are you referring to 110V?
Obviously if it's 240V, then the equipment will always be protected even if it's plugged into a non-RCD protected socket-outlet.
 
Can anyone tell me a PRACTICAL reason for installing RCD plugs to class 2 site equipment, and how do i PAT test the actual appliance without removing the RCD plug?

The RCD unit measures the current in the live and neutral using sensitive electromagnets.Where there is no fault condition, both readings will be equal.If you were to touch a damaged cable even on a class 2 appliance and provide a path to earth, the unbalanced current measurement would cause the RCD to trip, thus saving you from an electric shock, so they are fitted for a very good reason.
Hope this helps.
 
The RCD unit measures the current in the live and neutral using sensitive electromagnets.Where there is no fault condition, both readings will be equal.If you were to touch a damaged cable even on a class 2 appliance and provide a path to earth, the unbalanced current measurement would cause the RCD to trip, thus saving you from an electric shock, so they are fitted for a very good reason.
Hope this helps.

Good description but jut to add an example would be say a flymo mower it is class II but the extra layer of safety is if you have it plugged in to a RCD
 

Reply to RCD Plugs in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
466
I am a new PAT tester for a school, and I am stuck testing a plasma globe. It has a two core wire going to it, but no class 2 mark on the...
Replies
18
Views
2K
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
715
I purchased a new-build apartment 10 years ago, which came with a fitted oven and microwave. Both appliances are described by the manufacturer...
Replies
1
Views
732
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
540

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock