N
Nigel
I have just re-read the op.
The EICR that was done has highlighted a lack of RCD protection on final circuits on all CUs.
The client is trying to cut costs by asking if fitting ‘up front’ RCDs on the sub-mains instead of the CUs therfore installing five RCBOs rather than 40.
This is not an option due to selectivity so I would say no to that.
The EICR that was done has highlighted a lack of RCD protection on final circuits on all CUs.
The client is trying to cut costs by asking if fitting ‘up front’ RCDs on the sub-mains instead of the CUs therfore installing five RCBOs rather than 40.
This is not an option due to selectivity so I would say no to that.