Dave,
You were saying the supply needed RCD protection, you are now discussing RCDs on the load side two very different things!! If you want RCDs on the load side you do need ones that will work with a 110V supply voltage, ABB and others offer them, give ABB a call.
 
cheers mate, to be honest i was asked to rcd protect the site transformers, i ordered 50a rcbos to replace the 50a mcbs at the supply, they got back to me and said they didnt make them, so my mate called me and said put them in the tx, this confused me a bit and made me look deeper into it, ie now, i think they maybe would want the armoured rcd protected i would think as site transformers get moved and abused and a live cable could come out, in which case maybe i would have to mount a board adjacent to the main board and run the cables into this as i have 7 10 kva site transformerso install , unless anyone has better ideas.....how do i test the rcd on the load side if i install it
 
thanks, i was really after knowing the exact details, i e, L on L1 N on L2 and E on e.....at socket and then press test, as ive only ever plugged in the plug to the socket and pressed test.
 
Then with the greatest of respects what are you doing working on 400v and 110V systems? I have given you a link to a page that has at least 1 RCD tester that will happily do the tests that you require and you could not spot it. Are you aware of how badly things can go wrong when you short out a 400V supply? Do a youtube search for Arc Flash? What time curve are you selecting for the supply MCBs?
 
ha yeah, dont know.....didnt cover testing rcds on cte systems.....you have to start somewhere hey.....i put a 50a mcb into 1L3 in the board i worked to s spec, why do i need time curve.....its an armoured in the board to the tx...

- - - Updated - - -

its a single phase tx by the way
 

Reply to Rcd Protection For Supply To A Transformer On Construction Site? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Question is does this DB really need RCD protection as there are only internal lights and sockets supplying this large building that used to be a...
Replies
13
Views
376
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
736
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
799
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
723
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock