Discuss RCD Tripping Hell with high load in the The Welcome Forum area at ElectriciansForums.net

This won't help the OP with his problem, but what worries me is that he says the RCD had been bypassed. It is an RCD mainswitch - how exactly had it been bypassed?!?!?!

On 24hr board - RCD bypassed by Lin to Lout and Nin to Nout and relying on the white MEM DP switch as single means of isolation perhaps? (see #35 paras b and d)

Eco7 Board may be similarly bypassed - we are not told.

What 'this'?
 
Last edited:
Did you ever resolve this? My best guess is a loose N conductor in the meter / cutout, if everything else is ok.

Some people also presume they can test an appliance at the plug, but I'm sorry, a cooker, washing machine, dishwasher etc, have heating elements and motors that are only energised through a relay when the machine is operating. The ONLY way is for a clamp meter on the earth to measure earth leakage when these appliances are cycling through their operations.

I once had a dishwasher causing the RCD to trip. It was a break in the cable linking the door to the main body (I presume) as we managed to find it tripped in a certain position.

Love to take on your job but too far for me and you MUST have had it sorted by now. RCBO board would certainly help with this.

Also - final thought. You could have a shared / borrowed Neutral. You say you had an electrical test, but whoever did it failed to note the alien MCB in there, so I doubt he has done a thorough job. Has anyone undertook continuity / insulation resistance between all the neutrals? It's seldom done but very important.
 

Reply to RCD Tripping Hell with high load in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
581
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
843
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock